I am having a problem with the activated zone status that is being shown on the keypad (KP-06).
When I first upload the configuration all triggered PIR's will show correctly on the panel, However, after some time the display will revert to showing "kitchen kitchen kitchen kitchen " no matter what PIR or door is triggered.
I have checked the config thoroughly but cannot see any errors. Is this a bug in the system? and if so is there a work around?
I am using version 3.7.8.0 of the configurator.
On another subject - should I be able to ping the comfort from my PC via the eth3 module? I am managing to communicate with the Comfort via the configurator without any problems, but was just wondering if ping responses were blocked somehow?
Thanks in advance.
Avney
|
Posted: Tuesday Apr 1st, 2014 05:46 am |
|
2nd Post |
ident
Administrator
Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3493 |
Status: |
Offline
|
back to top
|
can you send us your cclx file to support@cytech.biz so we can take a look
You can ping your UCM/ETH03 from your PC using the IP address assigned by CS Manager eg ping 192.168.1.2
If you can communicate via Comfigurator then you can ping it
|
Posted: Thursday Apr 17th, 2014 08:53 am |
|
3rd Post |
Posted: Wednesday Apr 23rd, 2014 08:30 pm |
|
4th Post |
avney88
Member
Joined: | Wednesday Jun 19th, 2013 |
Location: | |
Posts: | 30 |
Status: |
Offline
|
back to top
|
Thank you.
I can confirm this Firmware has fixed the problem on my KP06 keypad.
|
|