Hi all,

I want to get a response from a zone input to send cyclically, the response is linked to a 1 bit on / off knx group address.

Please help:)



 Posted: Tuesday Oct 7th, 2014 04:10 pm
   PM  Quote  Reply 
2nd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

Use a Timer to repeatedly do a Response after a delay

eg
Zone Response = Response X


Response X
Do Response X after 10 seconds using Timer Y


This will cause Response X to repeat every 10 seconds (Change the value of the delay as required)

Assigning the Response X to the Zone Response means that the response is triggered by the zone activation

You will also need a way to stop this repetition from happening

Use action Stop Timer Y in a Response to stop this sequence. Stopoing the timer means that the target response will not get activated