Comfort Home Automation/ Security System Forums Home 
Home Search search Menu menu Not logged in - Login | Register

What have I broken?
 Moderated by: admin
 New Topic   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Saturday Jan 9th, 2010 05:04 pm
   
1st Post
Howser
Member
 

Joined: Monday May 22nd, 2006
Location: Pretoria, South Africa
Posts: 45
Status: 
Offline

  back to top

Hi,

I have Comfort Ultra 1 with (firmware 4.227) and while making a few changes to the AC restore location (we have a lot of power failures), I changed location 400 response. I think I broke something, the only difference I have observed is when a power failure occurs I hear a long beep instead of multiple beeps over the same period.

Any idea what location 400 response should be?

Regards
Mohau



 Posted: Sunday Jan 10th, 2010 02:20 am
   
2nd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 2133
Status: 
Offline

  back to top

Location 400 default value should be 4

You can also use Comfigurator 3 and do a selective write for Sound Types and Siren Types to restore these parameters back to their default values

Even if you dont use Comfiugrator, it shows you the locations and the values, eg Open the default file for your Comfort I Ultra,  Go to Security Types > Sound Types > Sound Types 3. The bottom left shows
(399) = 74, 4,0,4, 128

This means location 399 = 74, 400 = 4, 401 = 0, 402 = 4, 403 =128



 Posted: Sunday Jan 10th, 2010 02:24 am
   
3rd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 1412
Status: 
Offline

  back to top

The AC Restore Location is 736
In Events > Misc Events see AC Restore Response. The location of the Response is given in the bottom left. Response numbers are 2 bytes (low byte followed by high byte)



 Posted: Sunday Jan 10th, 2010 11:20 am
   
4th Post
Howser
Member
 

Joined: Monday May 22nd, 2006
Location: Pretoria, South Africa
Posts: 45
Status: 
Offline

  back to top

slychiu wrote:
Location 400 default value should be 4

You can also use Comfigurator 3 and do a selective write for Sound Types and Siren Types to restore these parameters back to their default values

Even if you dont use Comfiugrator, it shows you the locations and the values, eg Open the default file for your Comfort I Ultra,  Go to Security Types > Sound Types > Sound Types 3. The bottom left shows
(399) = 74, 4,0,4, 128

This means location 399 = 74, 400 = 4, 401 = 0, 402 = 4, 403 =128



Changed it back to 4, thanks for your help.

Last edited on Sunday Jan 10th, 2010 11:20 am by Howser



 Current time is 08:43 pm
Top




UltraBB 1.17 Copyright © 2007-2008 Data 1 Systems