Posted: Thursday Aug 2nd, 2007 03:31 pm |
|
1st Post |
Warby
Member
Joined: | Thursday Aug 2nd, 2007 |
Location: | United Kingdom |
Posts: | 101 |
Status: |
Offline
|
back to top
|
Hi
I have a ultra 2 panel with a UCM 485 controlling Dynalite. Whenever I am testing the interface is fine but once i have left something is happening which stops it from working. The only way to get Comfort controlling dynalite again is to Download the Config File.
Most of the responses are linked to a LSM and this is what i have been using to test (by winding the pot to full). The main function is triggering the outside lights from the outdoor PIR's.
We have another job with the exact same setup and there are No issues their.
Any suggestions?
Mark
|
Posted: Friday Aug 3rd, 2007 05:46 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
You will have to investigate whaty exactly stopped working
Is Comfort still working as normal, are you able to sign in and hear the voice etc
Is the UCM still working, are the D9 and D10 comms leds blinking fast?
What is the state of the ERR, Busy1, Busy2, RDT leds?
Use the Comfort Bus Monitor which can be downloaded from http://www.cytech-technology.com/temp/software/Comfort%20Bus%20Monitor.zip
This is a trool for monitoring communications on the Comfort Rs485 bus which can be a great help in identifying certain problems
|
Posted: Friday Aug 3rd, 2007 08:06 am |
|
3rd Post |
Warby
Member
Joined: | Thursday Aug 2nd, 2007 |
Location: | United Kingdom |
Posts: | 101 |
Status: |
Offline
|
back to top
|
I have had a play with it today as it has stopped working over night.
Comfort is working fine and the lights on the UCM 485 board are as follows. D9, D10 flashing rapidly. RDY is on and all other lights are off.
If I execute the response from Comfigurator it works fine and the LSM module appeared to be working fine last night (it was triggering the response when the pot was turned right up).
Most of the responses are as follows
If Flag Flag01 = 0 Then
If Input LSM <> 0 Then
Dynalite LinearPreset 2 32 0 0 255
Do BackDoorLsOff [Back Door Light Off] After 180 Seconds Using Timer04
End If
End If
Back door light is -Dynalite LinearPreset 2 32 5 0 255
There is also a linear preset message that is assigned to the LSM on and off responses.
We have a Ethernet UCM not a serial so is there any other way of using the Bus Monitor?
Thanks, Mark
|
Posted: Friday Aug 3rd, 2007 01:32 pm |
|
4th Post |
cytechboy
Member
Joined: | Friday Aug 3rd, 2007 |
Location: | Singapore |
Posts: | 6 |
Status: |
Offline
|
back to top
|
The Comfort Bus Monitor only works from the serial port at the moment
if you can trigger the Dynalite command from Comfigurator it means that the UCM must be working correctly. The D11 or D12 (the one that is red) led flashes when there is a mesage sent to Dynalite
So when the LSM triggers, there is no command to Dynalite?
Another way of monitoring is to use Hyperterminal and log in wit the correct IP address and Port number
Also you can use Wizcomfort in monitor mode with the IP address and port
You need to see the LSM Input being activated eg Message IPnn where nn is the input number in hexadecimal
|
|