Heatmiser UCM Functions
 Posted: Sunday Nov 17th, 2013 11:43 am
simond
Just installed the UCM/Heatmiser and integrating with my heatmiser network.
Couple of questions...
Firstly, can you put the thermostat in 'frost protection set back' mode? E.g. by setting the 'Thermostat' flag in comfort it turns the whole thermostat off - LCD and all... On the thermostats they have a 'power' button which when press turns off the program and turns on 'frost protection' mode, and the snowflake appears on the thermostat. This would allow me to 'set back' when going into vacation mode...
Secondly - I'm finding I often have to write values twice. For example I have 5 thermostats on the network (plus a NetMonitor, which was off during learn) and I have a a Response that sets the 'Theromstat' flag on them all off. I find if I run the Response it doesn't always hit them all, but if I run it twice it does. Any ideas?
Finally - 'Get Status' in Comfigurator is greyed out, so I can't see any status information....
Looking good though, another nice easy integration which makes life easier than using IR codes etc...
Cheers
Simon
 Posted: Monday Nov 18th, 2013 12:15 pm
The Frost Protection parameter is a Read only value
The Frost Protection setpoint temperature can be changed via a counter
There is another parameter Run Mode that can be changed (0 = heating, 1 = Frost Protect, 2 = Cooling) that may be used to change the mode. Currently it is not one of the parameters mapped to Comfort. We will see if that can work in the next firmware
For the problem of having to run responses twice, it may be the Netmonitor interfering on the bus. Can you remove Netmonitor and test is the error still happens
If it is due to Netmonitor, we may have to look other ways like repeat the transmission
 Posted: Monday Nov 18th, 2013 12:19 pm
simond
Thanks ident - that Run Mode parameter would be particularly valuable if it could be integrated.
Will do some testing without NetMonitor - do you know if it makes a difference if it is physically connected and powered down? E.g. the easiest thing for me to do is simply power it down but would it still leave a load on the rs485 network?
Cheers
Simon
 Posted: Monday Nov 18th, 2013 12:23 pm
Powering down should be OK, it should not affect the bus if properly designed
 Posted: Monday Nov 18th, 2013 05:44 pm
simond
I've now tried turning off the NetMonitor and its no different, most Responses need two 'shots' to get all the thermostats.
Is the heatmiser network topology important? I have 5 x Thermostats, 2 x UH-1 and 1 x NetMonitor. All the stats wire back to the UH-1's with them and the netmonitor wired in a daisy chain, with the UCM daisy chained on from the netmonitor via some structured cabling...
Thanks, Simon
 Posted: Tuesday Nov 19th, 2013 12:42 am
did you connect the 12V supply  from UH1 to the 12V into the Heatmiser plug in board? This provides an isolated 12V supply to the plug in module
When the 1st response does not work, which are the thermostats that see the command and which do not. Can this be isolated to the ones that are connected to 1 of the UH1s?
Why are there 2 UH1s?
 Posted: Tuesday Nov 19th, 2013 08:29 am
simond
Hi Ident
The UCM/Heatmiser I have I believe is an 'early' version that has the RS485 on the base board, thus has no separate 12V terminals... Could that be related?
The thermostats affected are not always the same, it seems variable. I would say first time I get 50% of the thermostats, and 2nd time I get the rest - but which ones are variable...
I have 2 UH1's as I have three Underfloor Zones and 2 Radiator Zones. A UH1 can only support one Radiator zone, so I have 3 UF and 1 Rad on one, and just 1 Rad on the other... I believe they are passive to the RS485 though?
Thanks for your help.
Simon
 Posted: Tuesday Nov 19th, 2013 11:38 am
HeFeng
Hi, simond,which firmware you are using for the UCM heatmiser,7.029,7.031 or 7.033? by the way, can you check your setting for heatmiser module about the output delay, temporary you can set to zero and see your response any difference...
 Posted: Tuesday Nov 19th, 2013 05:12 pm
simond
Hi HeFeng - thanks for the reply. I'm using 7.033 (have been since initial install). I can't seem to find an output delay setting - could you tell me where this is?
Thank you, Simon
 Posted: Wednesday Nov 20th, 2013 12:04 am
HeFeng
Hi, simond, maybe i made you confused, the heatmiser module out put delay is on module's optional setting,see below:
by the way, you can send your cclx file to support@cytech.biz, we can simulate your case.
 Posted: Sunday Nov 24th, 2013 08:05 am
simond
Thanks HeFeng - I've checked all the thermostats and they do all already have 00 as the output delay, so I've not made any changes here.
I've emailed in the CCLX file.
I'm also getting another issue which may be related. I'm finding some theromstats are turning themselves off, again individually and randomly, perhaps once a day or so. This is only happening when UCM/Heatmiser is connected to the network. It stops when I disconnect it... Sometimes when I turn them back on they get turned off again in few seconds. Could the registers in UCM/Heatmiser be getting corrupted by my programming and turn them off or something like that?
Thanks,
Simon
 Current time is 09:12 am