The spec is 6 A resistive load for each relay
Halogen lights are inductive and can cause an inrush during switching that can damage the relays so it is best to use 3 separate relays for this
Also you need snubbers or spark quencher for inductive load switching - this is a component which has 2 wires which should be connected across the load. We will send some to Laser with the next shipment
This post was moved to "Outputs" which seem,s to be the most suitable place