At 12:01 most days I receive a "Low Battery # Slave 1" Warning at 12:02 it restores.
Is this an issue in my configuration or something else?
Comfort II Ultra
Version 5.079
Rod McLeod
Attachment: Low Batt Warning Slave 1.jpg (Downloaded 26 times)
|
| Posted: Saturday Jul 24th, 2010 04:07 am |
|
2nd Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
The low battery Slave alarm occurs because the Battery connected to the Slave is weak, or is not connected.
There is an automatic Low Battery Test every 24 hours which switches off the AC supply to Comfort for 2 minutes. If a low battery condition is detected during that time on Comfort or any of the Slaves a Low Battery alarm is raised. When the low battery is detected the Battery test ends immediately and a Low Battery Restore event occurs.
The Low battery test interval is in Comfigurator: Configuration > Modules > Miscellaneous Settings. It can be disabled by setting the interval to 0.
A manual battery test can be started using the keypad F3,1. Subsequently the battery test will be at the programmed Time interval say 24 hours from this time.
If your battery has been installed for several years it may be time to change it.
Technical Note:
You can measure the battery voltage using a voltmeter by switching off the AC and keeping the battery connected. A good battery should be around 12 Volts. You should always measure a battery with its load connected. If the load is not connected, even a weak battery may show 12 Volts
|
| Posted: Saturday Jul 24th, 2010 04:17 am |
|
3rd Post |
EziAV
Member

back to top
|
I do not have a battery connected to the slave but I have one connected to the main panel. Because the slave is in the same cabinet I do not necessarily need a second battery connected to the slave? is this correct? If I do "Configuration > Modules > Miscellaneous Settings. It can be disabled by setting the interval to 0" as suggested, will this prevent the main battery from being tested as well? Last edited on Saturday Jul 24th, 2010 04:20 am by EziAV
|
| Posted: Saturday Jul 24th, 2010 04:34 am |
|
4th Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
The battery test is global so disabling the test will disable the test on Comfort as well
It is not true that if the slave is in the same cabinet that you do not need a separate battery. The purpose of the battery is to supply power to the alarm system in case of a power failure. In your case the slave would lose power and so would not work when there is a power faiulre.
|
| Posted: Saturday Jul 24th, 2010 05:04 am |
|
5th Post |
EziAV
Member

back to top
|
The slave can be powered also by the main panel if the via J10 connection, as it is in system. I assume this is OK?
If this is the case then the slave would be held up by the main battery connected to the main panel if a mains power failure were to occur.
Then if the above is correct and there is no battery and power supply connected to the slave it will still report low battery every time there is a battery test conducted.
Is there a way to still maintain the battery test function on the main battery with a slave board not having it's own battery and power supply?
|
| Posted: Saturday Jul 24th, 2010 06:21 am |
|
6th Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
The Slave can be powered from the Main Comfort panel using the 4 way connector. (J10 and J9 are the 4 way headers on Comfort 1 Slave). If that is the case you do not need to connect a battery to the Slave
However you must make sure that the current used by the slave and its 12V supply falls within the total of 1 Amp which the Comfort system can supply
|
| Posted: Saturday Jul 24th, 2010 06:42 am |
|
7th Post |
EziAV
Member

back to top
|
I have a SEM02 (PC01-008C) vF4.177 I can see JP1 12VDC Power Supply Terminal but I can not find a Battery Connection? Q1 If Comfort is drawing less than 1amp how could comfort be reporting low battery failure? Q2 There is no battery terminal that I can find on the SEM02 PCB so how can it report low battery failure on Slave 1 if you can not attach a battery? Last edited on Saturday Jul 24th, 2010 06:43 am by EziAV
|
| Posted: Saturday Jul 24th, 2010 06:59 am |
|
8th Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
SEM02 does not have a power supply or battery connector. I assumed you were referring to SEM01 which has its own AC supply and battery charger
In this case, the low battery may actually be due to Comfort not the slave as the Slave thinks it has a battery. The threshold of low battery reporting on Comfort and Slave would be slightly different so the Slave may report low battery at a slightly higher threshold than the main board.
How long have you had your system and when was the last time the battery was changed? - I assume the low battery warning was relatively recent. To check your battery, switch off the AC supply and measure the battery voltage while connected to Comfort. If the voltage is close to 11.5 Volts then it is time to change the battery
|
| Posted: Saturday Jul 24th, 2010 07:09 am |
|
9th Post |
EziAV
Member

back to top
|
I have done the battery check:
AC Power Off - Battery Voltage 13.5v
After 2min - Battery Voltage 12.49v
System has been installed about 2 years now.
Battery voltage seems fine above your 11.5v.
|
| Posted: Saturday Jul 24th, 2010 07:42 am |
|
10th Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
That seems fine
Can you measure the 12V at the SEM02 itself There may be a voltage drop for some reason
|
| Posted: Saturday Jul 24th, 2010 07:53 am |
|
11th Post |
EziAV
Member

back to top
|
Battery Voltage after 2min - 12.54
SEM02 Voltage after 2 min - 11.87
Connection cable 400mm long.
|
| Posted: Saturday Jul 24th, 2010 08:15 am |
|
12th Post |
slychiu
Administrator

| Joined: | Saturday Apr 29th, 2006 |
| Location: | Singapore |
| Posts: | 2133 |
| Status: |
Offline
|
back to top
|
It looks like the cable supplying the voltage to the SEM may be too thin resulting in a voltage drop. This could be because the SEM is supplying a lot of current
Increasing the cable thickness between Comfort and Slave would reduce the voltage drop. Also consider if you can supply the external devices from Comfort instead of the SEM so the current to the SEM can be reduced thus reducing the voltage drop
Doubling up the cable between Comfort and Slave would probably do the job
|
| Posted: Sunday Jul 25th, 2010 08:31 am |
|
13th Post |
EziAV
Member

back to top
|
Connected extra cable from SEM02 terminal JP1 back to Comfort, this solved the voltage drop issue.
Tested with manual battery test all OK
Tested with automated 12:01 battery test and all OK
Will replace battery as it is 2 years old as a precaution.
Thank you for your support in resolving this issue.