- slychiu - 10-02-2009

Please note that the FPR01 Controller has a DIP switch setting which may have been set to the wrong position at the factory

This DIP switch is near the connectors TD+, TR- etc

Positions 1,2,3 (RS485) should be ON
Positions 4.5.6 (Rs232) should be OFF
Positions 7,8 should be OFF

If the switch is not set correctly, there will be no communications between the UCM/Access and the Fingerprint controller

The FPR01 manual will be amended to document this is future



- slychiu - 10-07-2009

The FPR manual has now been updated and is now available for download here