CBUS activation on reset - phantom activation - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +--- Thread: CBUS activation on reset - phantom activation (/thread-455.html) |
- palmlodge - 02-04-2007 I had reported this in the CBUS forums as a couple of external lights are being turned on by something - we didnt know what. Now, I\'ve done some config changes today and I\'ve noticed that after a full download to comfort, when it resets \"says security off\" CBUS ids 34 and 36 are turned on (both lights on relay channels) Where should I be looking for what is causing this ? The \"startup\" response is NULL...is it Comfort ? Is it CBUS ? Is it the CBUSUCM ? - palmlodge - 02-04-2007 found it i think I have a dodgy outside magnetic door sensor for the side gates and it;s permantently open. i think comfort must be activating the automatic lights sequence as soon as it reboots... - slychiu - 02-05-2007 Remember that any active zone at reset will activate its ON response, as all zones are assumed to be OFF at reset |