Time incorrect by 24hrs - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +--- Thread: Time incorrect by 24hrs (/thread-4826.html) |
- Guest - 12-29-2017 On 22nd December I noticed that the time on a door station was correct but the day was shown as 23rd. I reloaded the schedule and ticked the option for \'set Comfort date and time\'. This put D&T correct, but 11 minutes later it reverted to the incorrect time, and has stayed there. For all I know this has been like this for a long time. Where do I start looking for the cause of this error? It is n Ultra 2 system file system 34, Comfort 7.099 - Ingo - 12-29-2017 I am guessing you have an Eth03 module and use NTP to sync time? Check the latest UCM/Ethernet and Eth03 firmware. Yes, they are different. Ult 7.099 is also a bit old, run the latest where possible. Ingo - slychiu - 12-30-2017 Yes, refer to this post http://www.comfortforums.com/forum113/4596.html ETH03 2.23 is the latest firmware for eth03 - Guest - 12-30-2017 Many thanks. I have installed the new version and the problem has gone away. Oddly though the version shown on the CSM has not changed from 2.1.0, so I assume that is the CSM version. Where is the ETH03 version shown for future referance? - slychiu - 12-31-2017 ETH03 firmware is seeen in Comfort Server Manager ETH03 GE 2.02 in the screenshot ![]() |