Problems with Comfigurator 3.12.13 - Printable Version
+---- Thread: Problems with Comfigurator 3.12.13 (/thread-5007.html)
- slychiu - 05-04-2019
Comfigurator 3.12.13 (Beta)
Known bugs
  • KP04AT Internal Temperature sensor field Read froom KP04 is not correct, does not update the sensor
  • Cbus Custom application 1 and 2, when Read from Cbus EEPROM, values of FF give exception.
  • Divide Action 157 shows Wring Parameters in Response Wizard
Bugs Fixed from 3.12.12
  • Action Code Counter clear and set  158,0 and 1 were reversed
  • KNX/Logic – when UCM/GSM4 is connected, scan gets exception
  • UCM/Logic add UCM give exception (not connnected to system yet)
  • Slave 1 comms failure is reported as Door station -15 in status bar
  • When connecting to a Comfort with a different vocabulary from the cclx file, Comfigurator detects the vocabulary correctly, but when selecting words, the wrong wordlist is used (according to the cclx file, not Comfort). However after saving the file and opening again, the correct vocab is used
  • KNX/Logic gets exception when UCM/GSM4 was connected
New Features and Changes
  • UCM/Modbus – allow different modbus id on each Modbus to Comfort line.
  • Added Action 160 s12V timed off to turn off S12V for programmed duration. (requires New Comfort Firmware to be released)
  • Added Subtract action 149, 3  subtract Immediate  Action. (requires New Comfort Firmware to be released)
  • Added Set user partition action 161 (requires New Comfort Firmware to be released)
  • Ucm/Pi module tab added virtual input assignment. If UCM/Pi is already in the configuration, delete and add it again to see the new Virtual Inputs tab
  • CM9001- EMS Sensors calibration allow decimal fraction (requires New Comfort Firmware to be released)
  • KP04AT temp sensor  - KP Internal Temp Sensor field for KP04AT with temperature sensor
  • C-bus 2 custom applications 1 and 2. Requires new UCM/CBUS2 Firmware (to be released)
- Swiss-Toni - 05-11-2019
I think their maybe issue with this version of Comfigurator, I spent the whole day trying to seup a system for a client yesterday and could not get keypads to work in partition, I am in the process of trying to find out what the keypads are!
I just tweaked my own setup and two things have occured
1) my KT03 display is now upside dow
2) there now seems to be an issues with the partitions on my own setup.
Will downgrade comfigurator and see if this resolves the problem.....
Downgraded comfigurator to 3.12.08 on my system and transfered files back to KT03 and comfort. Everything back to working as it should! Had to pull one of my older files out as the one I was using would not load as it had become corrupted (xml i think it said) when i went to use it on older version of comfigurator!
- slychiu - 05-12-2019
The new Comfigurator should not cause this type of problem. Do you have a file that has this issue, send it to support@cytech.biz
- wexfordman - 05-15-2019
Hi Slychui,
I am looking at the new velbus features in the latest version of comfigurator. Its a while since I altered my velbus config, so a bit of catching up to do.
I have looed to add a vmbgpo glass panel switch, and while I can manually add it, it only asks for one address, and there does not seem to be a way of mapping it to counters etc ? The VMBGPO uses I think 5 velbus addresses max.
A second note, is that I have a dimmer module which comfort des not seem to detect. It is on my velbus network, but when I press learn on the ucmvelbus, it does not detect it (or the vmbgpo for that matter).
- slychiu - 05-16-2019
The number of channels and Registers assignment is now determined by a configuration file \"velbus.cfgx\"It looks like the entry for VMBGPO is incorrect. It can be corrected quite easily. We will check, Is it 8 channel?
- wexfordman - 05-16-2019
There are 32 PB inputs, so thats 32 channels.
addresses also attached
- slychiu - 05-17-2019
Please go to File > Update Defaults. This wll update the configuration files inclduing the velbus file
After t his is completed, exit from Comfigurator and run Comfigurator again
You shoul dbe able to see 32 channels and select Map to Counter