Comfort to Dynalite problems
#4
The Comfort Bus Monitor  only works from the serial port at the moment

if you can trigger the Dynalite command from Comfigurator it means that the UCM must be working correctly. The D11 or D12 (the one that is red) led flashes when there is a mesage sent to Dynalite

So when the LSM triggers, there is no command to Dynalite?

Another way of monitoring is to use Hyperterminal and log in wit the correct IP address and Port number

Also you can use Wizcomfort in monitor mode with the IP address and port

You need to see the LSM Input being activated eg Message IPnn where nn is the input number in hexadecimal


Reply