C-Bus UCM
#11
What you describe does not make sense
If the SIM is plugged in correctly, it can send and receive from CBis
If it is not plugged in correctly, it cannot send or receive from Cbus

If plugged in correctly, the RDY (green) LED on the UCM should be on, and the BUSY1, BUSY2, ERROR (RED) leds should be OFF

See the attached photo for the correct pins to plug in


Attached Files Thumbnail(s)
   
Reply
#12
Hi ident

The the RDY (green) LED on the UCM should be on ( ITS ON AND NOT FLASHING )and the BUSY1, BUSY2, ERROR (RED)9 THE ERROR FLASHES EVERY2 SECONDS ) AND THE SMALL leds ON THE LEFT SIDE OF THE CBUS SIM FLASH EVERY 4 SECONDS THE LEDS ON THE RIGHT OF THE SIM (GREENAND RED FLASH VERY FAST..
not sure whats happening here but... the c bus sim is plugged in corectly and no joy

i tried the phone login and i still et communication error 18 ??

Buy the Way Error 2 Stays on
Reply
#13
If the ERROR led remains on it means that it is not detecting Cbus

Are the SW7 shunts are set correctly for UCM #2 ie A removed, and others B to D inserted and are the D9 RED led and D10 (green) leds both flashing?
If the D9 and D10 leds are not flashing that means the ID is incorrect

The shunts may be having poor contact. Try using shunts from elsewhere
Do a Scan for UCMs in Comfigurator Modules Tab
Reply
#14
The ID Seems Correct As D 10 And D 9 Are Flashing On the C Bus UCM And On My Unicersal UCM..I Have Tried New Jumbers on the SW 7 A Removed B inserted And c inserted
As For Comfigurator im Still using Mindit V 2.0
As My Local Clipsal Supplier insists In MIND it
i Have
Comfigurator Latest . Do You Sugest i Try It ?
Also Can i Flash the Firmware ? Maybe it Will Help ?
Reply
#15
The ID Seems Correct As D 10 And D 9 Are Flashing On the C Bus UCM And On My Unicersal UCM..I Have Tried New Jumbers on the SW 7 A Removed B inserted And c IS NOT inserted D 3 Stays On And D 1 Flashes Randomly
On The SW8 Side A And B Are inserted



As For Comfigurator im Still using Mindit V 2.0
As My Local Clipsal Supplier insists In MIND it
i Have
Comfigurator Latest . Do You Sugest i Try It ?
Also Can i Flash the Firmware ? Maybe it Will Help ?
Reply
#16
You will have to explain more clearly what exactly is your configuration.

What is the UCM/Cbus ID?
What is the UCM/Universal ID?

You say you have A not inserted, B inserted, C not inserted in one of the posts
This is an ID of 6!
How many UCMs do you have? and does it correspond with the Number of UCMs in Mindit?

You say you have Communications Failure 18. This means UCM ID2 is not communicating

If you have D9 and D10 leds flashing on the UCM/Cbus then it should not be the UCm which is failing to comunicate

You may have a clash of UCM IDs. You must not have 2 UCMs with the same ID
Make sure each UCM is set to a unique ID 1,2,3 etc and there must be no missing Ids ie you cannot have ID1, and ID3 with no ID2



I dont think flashing the firmware is going to solve the problem if it was working
before you removed the SIM. Mindit V2 does not support flashing anyway


Let us have ALL the products and their firmware version in your system

Mindit firmware?
UCM/Cbus firmware?
Universal Firmware? Are you sure you have  this type of UCM as it has not been released formally? Do you mean a normal programming UCM ?



Reply
#17
Perhaps thsi Can Help


Attached Files Thumbnail(s)
   
Reply
#18
The photos do not help much
Can you answer the questions I asked in the previous post please?
Reply
#19
Hi ther ident
unfortumately i Do Not Know the ID And Shunt Requirements
but I Seem Yo Have Lost The Communications error 18
and can Arm The Alarm Via Telephone Now.

The System Was Working Perfect For 3 Years Not one Glitch
Then While doing a Plumbing Change in The Ceiling i Hooked The C Bus Cable. So i Cut the Power Off And Reset From There No Cbus To Minder/Comfort..

I Installed Comfigurator 3 And Got the Following


Exception while reading vocab.cfg:
System.Exception: Error reading C:\\Program Files\\Cytech\\Comfigurator 3\\Config\\vocab.cfg: Could not find file \'C:\\Program Files\\Cytech\\Comfigurator 3\\Config\\cs-wl-th.cfg\'.
at Comfort.Vocab.AddWordLists(Configuration configuration, String filename, List`1 wordlists)
at Comfort.Vocab.GetWordLists(Configuration configuration)
Reply
#20
Can you get someone on site to take a look at your setup?
It may be too difficult to find out enough info from here
Reply