I needed to temporarily disable a zone/input as I have a problem with the sensor. I can\'t find anything in the manual or on the forum but have concluded that you can use the DigitalNC/DigitalNO zone types to do this. The steps I took where
Make sure you have saved the current configuration
To temporarily disable a circuit change \'Zone Type\' in Zones/Inputs to DigitalNC [30]/DigitalNO [31] - to reflect the sensor type NO/NC
Write this to a new configuration file - I used an extension of int for intermediate
Then Transfer/Write (PC -> Comfort)Alarm circuit to test
When the sensor issue is resolved then the old configuration should be restored