OK there is far more to it than this
Is your smoke head latching or non-latching - this will determine how it is (or can be ) set up within comfort.
(I think i have this the correct way around) The lathing heads hold onto the NC contact until the power to them is broken. If you use a non-latching head then you do not need to reset S12V as the head will re-trigger (not latch) after a short time. If there is still smoke present it simply stays active if the smoke has gone it 'resets and thus negates the need to reset the head from comfort - comfort of course will stlil need a sign in to clear the smoke signal.
ALSO you may need to add the EOL resistors to allow reporting of different states.
Now you have asked the question I will take another look and provide a full explanation in the smoke section ( over the next few days as i will need to bench test again as i always forget !)
The there is another scenario with multiple heads in series etc
Hope that this helps (nudge me if you don't see another post in the next few days)