slychiu wrote: The is a useful connection diagram, did it comne from us?

Not really; I pieced the info needed together from the comfort Hochiki diagram, the Apollo manual and a phone call with an Apollo tech.
For future reference this detector base and series works well with Comfort:https://www.apollo-fire.co.uk/products/range/series-65/relay-bases/45681-508apo-series-65-12v-relay-base
They default to non-latching and reset themselves, behaviour was perfect with the alarm sounding continuously for as long as there was smoke and resetting on its own, no need for jumper changes from default on either the detector or Comfort. 
Only tested this in one detector per zone config but this wiring should work for daisy chaining too:
Comfort to Detector:Comfort +12V to Apollo PCB 12VComfort Power Com to Apollo Edge L1InComfort zone wire to NC on Apollo PCBComfort zone wire to C on Apollo PCB
Last Detector Termination:2K7 Resistor L1Out on Apollo Edge to Apollo PCB 12V (Need this for it to work at all)4K7 Resistor between NC and C on Apollo PCB (This seems to allow detection between alarm and wiring fault)
Comfort Zone set to Fire NC