 Posted: Friday May 17th, 2019 09:42 pm
 PM  Quote  Reply  Full Topic 
Swiss-Toni



Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 349
Status: 
Offline

  back to top

I have installed a controil; panel and a Sem for a client, the problem is that the zones are not responding as they should. The SEM is connected via cat cable as per manual. the Zones that are affected in the SEM are 17/18 and 23/24 when used they show Inactive /active  and fail to change accordingly, initialy I changed cabels testing contacts and Pirs, only to find the fault was directly on the SEM as it was tested directly by linking out zones and leaving open. Siminlar situation is occuring on Control Panel Zone 1,7, & 8.I swopped the SEM for another that I had and still the same problem occured, this leaves me to think that the problem is either the Control Panel is faulty or their is a serious fault in the programming.The system has been set up as an alarm only system so far and has been staged with 3 partitions.
Has anyone had any similar problems and were you able to resolve the problem
Cables and end products have been changed unecsearily to no avail, after which all end equipment has been tested working inc cabling.