LEM01B and LEM02B can configure EOL resistors for CM9001 in the same way using Comfigurator . Zone > EOL settings as shown above.
However the older LEM01-M2 and LEM02-M2 and LEM03-M2 has physical EOL zone shunts. It is best that these older LEMs are used with CM9000 instead of CM9001.
If LEM0x-M2 is used with CM9001, then Comfigurator will not have the EOL settings for these LEM zones as Comfigurator knows that the LEM has zone shunts. In such cases you must use the zone shunts to select EOL resistor for the LEM