david8811 wrote: Hi Mr Chiu,
I have programmed my zones 25 to 30 to bypass zone using SwitchNO response. There have been working fine for the last 2 years or so. However, last 2 or 3 weeks I realized that bypass switches are no longer working. Now, the system announces these zones as "zone Trouble". As a result, I cannot arm the system. Appreciate your support.


Zone Trouble means there is a problem with the zone wiring. eg brokenm wiring. Are these zone using EOL resistors? What is the EOL shunts position on these zones. If there are wrng eg set to Double EOL position but the EOL resistors are not connected then you will have zone trouble.
if the shunts are set to NO EOL,. then you can test by disconnecting the zone wires from the zones. and connecting a wire to short and Open the zone, Do you get Zone Trouble?