What a fast answer ! :)

Thanks for the clarification about sending the counter state to KNX.
So the loopback "Comfort to KNX" -> "KNX to Comfort" is not possible, thank you for pointing that out too.

So another possibility could be :

1) Keep the UCM/KNX normal configuration and behavior (for example, line cut sends event to KNX 1/1/1 address) - no loopback trick to store values in counters
2) For the desired comfort events, assign the action to update a counter with the event value (i.e. the "line cut" event would update counter001), this is totally independent of KNX
3) Add a "KNX to Comfort" address (2/1/1) that will trigger the sending of all counter values to KNX bus (in my example counter001 value would be sent to 1/1/1)

The "2/1/1 response" will have to send all counters values, one after the other (max 10 messages at the time).

Does that make more sense ?