Smoke Detector Reset
 Moderated by: admin
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Friday Aug 18th, 2006 04:37 am
   PM  Quote  Reply 
1st Post
Scott James
Member


Joined: Tuesday Aug 8th, 2006
Location: Melbourne, Australia
Posts: 30
Status: 
Offline

  back to top

Hi, does anyone know of a way to reset the smoke detectors S12V output upon sign in.

IE: when the smoke detectors are triggered, You need to sign in to acknowledge the alarm and you also need to turn off the S12V output for a second or so to reset the smoke detector.
(and bypass the input while turning off th S12V output to avoid hearing zone trouble)
Otherwise the smoke detector keeps going.
Does anyone know of a way to reset the S12V output upon the signin after a smoke alarm?


Thanks



 Posted: Friday Aug 18th, 2006 04:53 am
   PM  Quote  Reply 
2nd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

There is a default response which switches off the S12V output then switch on  again after 3 seconds using a timer, see the attached screenshot

This can be assigned to the System Disarmed or System Armed Response or to a Home Control Menu
It is recommended that you do not reset  the smoke detectors on disarm, because if an alarm occurs, you may disarm to turn off the sirens if it is a false alarm, and the information about which smoke caused the alarm would be lost

Attachment: S12V Response.jpg (Downloaded 59 times)



 Posted: Friday Aug 18th, 2006 05:38 am
   PM  Quote  Reply 
3rd Post
Scott James
Member


Joined: Tuesday Aug 8th, 2006
Location: Melbourne, Australia
Posts: 30
Status: 
Offline

  back to top

I already have the responses written to  bypass smoke input, turn off s12V turn backon S12V after 5 sec and then unbypass smoke input. Buy I want to run ths upon sign-in.
It is no good to assign it to system disarm because if Comfort is not armed at the time that the smoke detector is triggered it will do nothing, because it will only work when coming from an armed state.


If I could some how run my reponse upon a valid sign-in it would be great.

Then I could set the ALARM TYPE - FIRE to set a flag,
and then check that flag at sign-in and then run my response.


I think I might be trying to do something that cant be done.

Thanks

 

Last edited on Friday Aug 18th, 2006 07:29 am by Scott James



 Posted: Friday Aug 18th, 2006 08:04 am
   PM  Quote  Reply 
4th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The system disarmed alarm is also activated when Comfort is disarmed following any alarm, including a fire alarm, hence this will work even when Comfort is not armed

Checking alarm type would be no good because the alarm type when you disarm is System Disarmed

There is no response activated when you sign in

regards



 Posted: Friday Aug 18th, 2006 12:01 pm
   PM  Quote  Reply 
5th Post
Scott James
Member


Joined: Tuesday Aug 8th, 2006
Location: Melbourne, Australia
Posts: 30
Status: 
Offline

  back to top

Ahhhhhhhhhhhhhhhhhhhhhhhhh, Thanks! :)