Output Current Limitation 300 mA
 Moderated by: slychiu
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Saturday Sep 24th, 2011 02:11 pm
   PM  Quote  Reply 
1st Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

Each set of 8 outputs on Comfort Controller, LEM01 or Slave is limited to 300 mA total

This is limited by a resettable fuse which protects the outputs against damage
The resettable fuse will recover when the excessive current is removed

Use outputs on different modules to split up the current load



 Posted: Saturday Mar 10th, 2012 09:46 pm
   PM  Quote  Reply 
2nd Post
lwillerton
Member
 

Joined: Sunday Oct 2nd, 2011
Location:  
Posts: 221
Status: 
Offline

  back to top

hi ident

hope you can help again. I would like to use the outputs to power up leds.

1, i would like to use a tri colour led on a couple of doors.

LED off, alarm state off,

LED green, zone bypassed

LED red, zone not bypassed.

2 i have a couple of ir beams in the garage so when beam is broken it triggers leds which are basically act like traffic lights.

beam one broken green led lights

beam one and two broken amber led lights

beam two broken red led lights.

can I power the leds directly from the output or do i need to do some electronice to drop voltage / current.

Cheers

Lee



 Posted: Sunday Mar 11th, 2012 01:19 am
   PM  Quote  Reply 
3rd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The outputs will go to 0V when it is turned on, so there wil be 12V betwen the center Common 12V terminal and the output terminal

You can use this voltage to drive LEDs but you wil need to connect a resistor in series depending on the voltage and current specs of the LED

Try adding a 2.7 K resistor provided for use for EOL resistors. If the LED is too  dim use a lower resistor value



 Posted: Sunday Mar 18th, 2012 08:33 pm
   PM  Quote  Reply 
4th Post
lwillerton
Member
 

Joined: Sunday Oct 2nd, 2011
Location:  
Posts: 221
Status: 
Offline

  back to top

Hi All,

I have managed to get this idea 50% working.

I have used a bi colour LED which has 2 anodes and one cathode. the problem with this is the O/P drop to 0v and the common remains at 12v so I believe  this will not work and needs to be the opposite way round. I have tried all combinations I can think of, and the only configuration I can get working is one side of the led (either red or green) not both.

Any ideas? I guess the only other way is to use 2 LEDs rather than I bi colour.

The positive is I do get the logic to work so that the LED will light when bypass is enabled.

This is such a flexible system I love it. 

Cheers

Lee 



 Posted: Monday Mar 19th, 2012 02:01 am
   PM  Quote  Reply 
5th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

Try looking for a bicolour led with 2 cathods and 1 anode



 Posted: Sunday May 6th, 2018 05:39 am
   PM  Quote  Reply 
6th Post
davids
Member
 

Joined: Saturday Aug 26th, 2006
Location: Melbourne, Australia
Posts: 54
Status: 
Offline

  back to top

I am having an issue with my relay outputs to my sprinkler zones. I have had a 1 amp 24 VAC power supply operating just fine for 10 years but now I keep blowing the power supply fed to my relay outputs because it seems that the sprinkler solenoids are drawing more current than they used to.
If currents were limited to 300 mA by Comfort then I would have thought that it would not have been possible to be drawing excessive currents that keep blowing my power supply.

The only strategy seems to be to go for a power supply with a larger current rating but will I be limited by what Comfort can drive? 
David:X



 Posted: Sunday May 6th, 2018 06:04 am
   PM  Quote  Reply 
7th Post
Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 349
Status: 
Online

  back to top

Are you refering to RLY10H or (other relays direct output as it should not blow and fuses that you describe relays are zero voltage direct output 300ma!
YOu need to use a multimeter to see what the voltage is on sprinkler system, disconect from comfort and test each component, lond winded process but the most effective way



 Posted: Sunday May 6th, 2018 06:04 am
   PM  Quote  Reply 
8th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

You say that your external power supply 24VAC 1 Amp is the one that is damaged by the solenoid

Comfort main board limits the current to the Relay Coil to 300 ma ie the input of the relay. This is not related to the current from the external power supply

If your power supply is damaged by the solenoid, this is completely isolated from the coil or Input of the comfort relay. It is a problem with the external power supply not being able to drive the solenoid.



 Posted: Sunday May 6th, 2018 08:58 am
   PM  Quote  Reply 
9th Post
davids
Member
 

Joined: Saturday Aug 26th, 2006
Location: Melbourne, Australia
Posts: 54
Status: 
Offline

  back to top

Thanks for that information.Before I source a different power supply I just wanted to check if I might encounter any issues with Comfort.Glad to know that the solenoids drawing more current is independent of Comfort. 



 Posted: Monday May 7th, 2018 06:50 pm
   PM  Quote  Reply 
10th Post
Craig Robins
Member
 

Joined: Monday Mar 3rd, 2014
Location:  
Posts: 43
Status: 
Offline

  back to top

Before you change your power supply for a larger one, you might want to check the wiring to the solenoids. If there is a short, it would account for your problem and would not be solved by uprating the supply.



 Posted: Sunday May 13th, 2018 09:10 am
   PM  Quote  Reply 
11th Post
John W
UCM Pi Users
 

Joined: Wednesday Feb 18th, 2009
Location: United Kingdom
Posts: 107
Status: 
Offline

  back to top

You might find that while the cable doesn't look damaged,it's insulation is breaking down.
Disconnect it and stick a meter across it to check the core to core resistance. If you have a megger insulation tester disconnect all devices and try with that.