Comfort  Automation/ Security System Forums Home
Home Search search Menu menu Not logged in - Login | Register
Comfort Automation/ Security System Forums > Support > Problems & Troubleshooting > Firmware Upgrading Problems > Problems with Upgrading firmware by UCM Programming Cable

Problems with Upgrading firmware by UCM Programming Cable
 Moderated by: ident
 New Topic   Reply   Printer Friendly 
 Rating:  Rating
AuthorPost
 Posted: Tuesday Sep 27th, 2011 02:21 pm
   PM  Quote  Reply 
1st Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The procedure for upgrading Comfort controller or other modules using the UCM Programming cable is illustrated in  http://www.comfortforums.com/forum4/1216.html along with pictures. Please read this topic before continuing.

Most problems with doing this upgrade are due to incorrect connection of the programmming cable.


The end of the cable with two connectors with 4 wires (PP1) and 2 wires (PP3) must be connected to the UCM doing the upgrading, and the end with just the 6 way connector must be plugged into the module to be upgraded. Many users connect it the other way or loop back the 6 way connector to the UCM end.

The PP2 header must be shunted during the upgrade

The correct connection for upgrading Comfort is shown below



Another point is that the upgrade cannot be done with Comfort connected to a battery alone, without an AC input, as may be the case in a new house where the power supply has not been turned on. You need to have the AC connected as well. The battery need not be connected



 Current time is 08:28 pm
Comfort Automation/ Security System Forums > Support > Problems & Troubleshooting > Firmware Upgrading Problems > Problems with Upgrading firmware by UCM Programming Cable
Top




UltraBB 1.172 Copyright © 2007-2014 Data 1 Systems