Hi, Just quick questions on something which will probably be simple but I cant figure out.
I have two external sounders both of which I want to connect to my SEM01-M2. As these are different makes I want to connect straight back to the outputs on the board.

Is this OK to do or will I need to use the 'self contained bell' feature they both have? They both have batteries. I would prefer not to do this as both say it will have an effect on the volume of the sounder.  They use 480mA typical with siren and strobe.

Both units only have one output for tamper. How do I use this to close the circuit on the main board? Do I use 2 wires on the permanent negative and put one back to the other connection on the tamper terminal?

Sorry if these are common sense, I almost feel I should create another user on here for my 'less than intelligent questions'!

Thanks in advance,
Chris.



 Posted: Monday May 14th, 2012 09:12 pm
   PM  Quote  Reply 
2nd Post
wiredhome
Comfort Distributors


Joined: Thursday Apr 12th, 2007
Location: Dublin, Ireland
Posts: 81
Status: 
Offline

  back to top

Hi Chris

If you scan and pm me the wiring diagrams of each unit
I will work out the wiring to Comfort for you

If you set them as SAB's then there is no effect on the volume

regards
Niall



 Posted: Tuesday May 15th, 2012 08:40 am
   PM  Quote  Reply 
3rd Post
Vangelis
Member
 

Joined: Tuesday Jan 31st, 2012
Location:  
Posts: 138
Status: 
Offline

  back to top

I am planning to do the very same with my setup, as I want two active external sirens.

From recollection, if being sourced from the same output, in SAB mode,then you will be pulling close to 1Amp (in your case) in an alarm condition, which might be a strain on the output.

SCB as you say will use the internal battery (of the bellbox) to drive the siren / strobe with reduced volume, but you will not have the loading issue on the output.

One thing you may want to consider is the age of the existing alarm sirens - as if previously configured in SAB mode, and you then change to SCB, you will be putting more strain on a potentially old battery.

As for the tamper wiring, I am sure there was information regarding this being wired in series with each bellbox and back to the enclosure tamper circuit in the documentation section of this forum.

Vangelis



 Posted: Friday May 18th, 2012 11:51 am
   PM  Quote  Reply 
4th Post
strickers
Member
 

Joined: Sunday Jul 24th, 2011
Location:  
Posts: 78
Status: 
Offline

  back to top

Hi,
Thanks for your responses. I have attached my two bell boxes wiring diagrams. As you can see they both only have one output for the tamper so I assume this is quite common.
Can you please let me know how I complete the tamper circuit? Do I just connect the other one to the common negative?
Thanks in advance,
Chris.


Attachment: Sounder wiring.pdf (Downloaded 8 times)



 Posted: Friday May 18th, 2012 01:17 pm
   PM  Quote  Reply 
5th Post
wiredhome
Comfort Distributors


Joined: Thursday Apr 12th, 2007
Location: Dublin, Ireland
Posts: 81
Status: 
Offline

  back to top

Hi Chris
can you scan the full sheet and i will do you a full diagram
including how to series the tampers
regards
Niall



 Posted: Wednesday Feb 15th, 2017 07:06 pm
   PM  Quote  Reply 
6th Post
strangehead
Member


Joined: Monday Feb 13th, 2017
Location:  
Posts: 2
Status: 
Offline

  back to top

Last edited on Wednesday Feb 15th, 2017 07:11 pm by strangehead



 Current time is 09:35 am
Top




UltraBB 1.172 Copyright © 2007-2014 Data 1 Systems