Hi

As per a recommendation from a Comfort installer , I've got 2 Hochiki smoke detectors.
DFJ-AE/3 Hochiki Conventional Fixed Temperature Heat Detector (60°C)
SLR-E3 Hochiki Conventional Photoelectric Smoke Detector

along with the following base to attach each of them to - YBO-R/6R Hochiki Conventional Latching Relay Base
I've run a wire for each back to Comfort, but could do with some recommendations on how best to wire them into Comfort and/or each other? also how best to configure them in Comfigurator.

Any help most appreciated.



 Posted: Wednesday Oct 2nd, 2013 06:22 am
   PM  Quote  Reply 
2nd Post
Home
Comfort Distributors
 

Joined: Wednesday Jul 12th, 2006
Location: United Kingdom
Posts: 771
Status: 
Offline

  back to top

I'm working away at present - Ill do a page on this later tomorrow.



 Posted: Wednesday Oct 2nd, 2013 06:34 am
   PM  Quote  Reply 
3rd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

For Comfigurator, use Zone Type Fire N/C (Normally Closed) assuming the detectors have a normally closed output



 Posted: Thursday Oct 3rd, 2013 07:55 pm
   PM  Quote  Reply 
4th Post
Home
Comfort Distributors
 

Joined: Wednesday Jul 12th, 2006
Location: United Kingdom
Posts: 771
Status: 
Offline

  back to top

OK its been a while

You need the latching base (as opposed to the non-latching base). The latching base will reset every few minutes so there is no need to ass a break to the 12v power to the sensor.

If you have the non latching base then you will need to wire the +12V into the S12V terminal - there is then a response that allows you to break the power to allow the sensor to reset.

You should use EOL as well + you can wire an LED or similar a the main panel - all of this is really prompting me to create a 'proper' written summary because there are a number of different ways of doing things.....