I am using 3 SEM complete with 4 LEM, i plan use sensors and devices third party connected to the output about more than 20 : microwave sensor, selenoid valve, relays, IR Fence beams..
1. Its possible to power all devices connected to comfort that need  external power by powering them from  12V / S12V port , isnt it ?
2. I read about this port only powering maximum 1 amp for all devices connected to controller or SEM ..This is limitation for one SEM or for all devices connected ?

Last edited on Sunday Aug 23rd, 2015 04:04 pm by

tech07
Administrator
 

Joined: Thursday Jan 29th, 2009
Location: Singapore
Posts: 106
Status: 
Offline

  back to top

I am using 3 SEM complete with 4 LEM, i plan use sensors and devices third party connected to the output about more than 20 : microwave sensor, selenoid valve, relays, IR Fence beams.. 1. Its possible to power all devices connected to comfort that need  external power by powering them from  12V / S12V port , isnt it ?
Yes. Power from 12V S12V can be switched off and on by response so be careful
2. I read about this port only powering maximum 1 amp for all devices connected to controller or SEM ..This is limitation for one SEM or for all devices connected ?
Eacch comfort and SEM can supply 1 AIf you have Comfort and 5 SEM then it can supply 6 Amps

Last edited on Sunday Aug 23rd, 2015 04:07 pm by tech07

bagushandhoko
Member
 

Joined: Saturday Jul 25th, 2015
Location: Jakarta, Indonesia
Posts: 91
Status: 
Offline

  back to top

Thanks

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Sound like you are looking at adding a lot of 12v equipment.Why not get a seperate 12V supply and reduce the risk of drawing to much power away from comfort, here is a link that should give you an idea of what to get. http://www.ebay.co.uk/itm/9-Way-Port-10A-12V-CCTV-PSU-Power-Supply-Cabinet-Box-for-Camera-System-Kit-/111562346870?hash=item19f9a25176 Depending on your requirements you can get different panels with more or less terminals and also idfferent amp output ratings. You can also get rack mounted 12v psu (these tend to be extremeley expensive though)

Last edited on Saturday Aug 29th, 2015 10:43 pm by Swiss-Toni

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

If alarm sensors are to be powered by external 12V, these should also be battery backed up
Comfort will report power failure and low battery on its own power as well as its slaves, which is more convenient

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Had a system crash green lights on sem and main board none of the components are lit up at all RPI GSM Ethernet. it looks as though no power is going to them at all as is the SCS swiches & RIO01 

Cant figure out why it wont supply power tried addint independent power on ethernet powered up for a few seconds and shuts down
Any ideas

Last edited on Thursday Aug 29th, 2024 07:31 am by Swiss-Toni

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

How about the leds on the main comfort? Can you check the 12V output from the 12V and COM from Comfort?

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

The green is iluminated on the main comfort will check power on the 12v com now

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Green LED is flashing nothing on the red, the reading is .491V on the 12v/com

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

There may be overcurrent or short circuit on the 12V output supplying slaves and keypads etc  This causes the voltagfe to go to the low level you measured. Remove all dvices eg UCM, Keypads etc that use 12V from Comfort, then check if the 12V recovers. You may have to wait a few minutes as the resettable fuses must cool down before the voltafg can recover

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Getting a reading of 1.3v of the transformer

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

slychiu wrote: There may be overcurrent or short circuit on the 12V output supplying slaves and keypads etc  This causes the voltagfe to go to the low level you measured. Remove all dvices eg UCM, Keypads etc that use 12V from Comfort, then check if the 12V recovers. You may have to wait a few minutes as the resettable fuses must cool down before the voltafg can recover
The reading is with everything removed already, done that yesterday Im thinking that a complete power down to coll it down ect

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

The old big transformer or the new DC15 V power supply?
  Are you measureing DC or AC. If you use the big transformer you should measure AC, If using the new Meanwell dc supply you should measure DC

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

With the sem disconected and the ethernet conected to the Sem the ethernet lights come on but as soon as connected to main board it all shuts down

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Its the old big transformer

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

maybe a fault on the SEM. check if the system works without sem

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

System does not with the sem disconected, i replaced the sem board yesterday will try the old one back in there in all likelihood I would say it was the main board that is knocking everything out

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

I believe I have located the fault, although everything was disconected I realised that there was a black and red cable connected to the 12V/COM which I overlooked. Removed the cable and reconnected the ethernet & RPI which both then fired up, these cables have never been touched in the last ten years so I will replace those and let you know tha outcome in a few days. Thanks for your insight :cool:

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

as I suspected. Good that yu found ito

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Have mangaged to get it u and running for the most part, however cannot quite get the scs6 to stop flashing once they are pressed, the same programming has not changed and they do work to a point some things still not responding which I will takle later on but how do I get the scs6 led lights to stop flashing anyone know, its not a case of removing the power from the scs6 and putting back! this seems to have developed as a fault on all of them

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

SCS leds stop when the leds get a command to turn on or off. I would look at your scs responses

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

slychiu wrote: SCS leds stop when the leds get a command to turn on or off. I would look at your scs responses
 The issue is that comfigurator now does not give you the option to do scs resposes, this is using the latest version of comfigurator I need the range up to 200+ not starting at 200+

Attachment: Screenshot (110).png (Downloaded 7 times)

Last edited on Friday Aug 30th, 2024 06:41 am by Swiss-Toni

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

Swiss-Toni wrote: slychiu wrote: SCS leds stop when the leds get a command to turn on or off. I would look at your scs responses  The issue is that comfigurator now does not give you the option to do scs resposes, this is using the latest version of comfigurator I need the range up to 200+ not starting at 200+  Because of this I cannot programme the RIO01 or the SCS switches 4 X RIO01 & 7 X SCS6 switche. Even using original file that was working previously it will not allow for it to work. Is it possible the NVM IC could be the issue Im sure there is a back up wich I will swop around if I have it

Last edited on Friday Aug 30th, 2024 06:48 am by Swiss-Toni

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

in Comfigurator can you go to File > Update Defaults. Then restartr comfigurator/ This fixes a configration error in RIO/SCS
T

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

That fixed virtually every fault after hours of head scratching ha ha ha ha, thank you ;)

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

yes we documented here http://www.comfortforums.com/forum84/5500.html