Hi all,
I tried (and failed) with the UCM/ZWave module - mainly as I misunderstood the concept of it's workings...
So I now have UCM/Eth2 interaction via serial cmds working, and was wondering if I could do the following...?
I have a ZWave door sensor on the front door, and want to have this trigger the entry / exit delay of Comfort.
This currently reports it's 'state' to my HA and I can have this issue a Serial cmd to Comfort - bit I am unsure about is what cmd to issue (basically simulating the activation of a virtual entry/exit zone via serial cmd)
Any ideas?
Vangelis
|
Posted: Thursday Aug 27th, 2015 04:26 pm |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
If you have UCM/Zwave3, this can be by done by creating a virtual node associating the Door sensor to it, and mapping to a Virtual Zone.
The door sensor becomes a virtual Input say Zone 1. Program Zone 1 as Entry Door zone type. When the door sensor opens, this will start an entry delay just like a physical zone.
Virtual Inputs are possible by KNX and Cbus UCMs where group addresses can be mapped to virtual nodes
With UCM.ETH and without UCM/Zwave this is difficult
One roundabout way is to connect an unused Output eg Zone 10 in Comfort to a Zone Input programmed as Entry Door. Send the command O!0A03 to Pulse Output 10 for 1 second (ie open and close the door)
This will start an entry delay
|
Posted: Thursday Aug 27th, 2015 05:11 pm |
|
3rd Post |
Vangelis
Member
Joined: | Tuesday Jan 31st, 2012 |
Location: | |
Posts: | 138 |
Status: |
Offline
|
back to top
|
Thanks Slychiu
I never got the UCM/Zwave working as it should, however I like your sneaky way of using a Pulsed Output