In UCM/Modbus Properties, set Modbus Master/Slave as Slave. Modbus Slave ID in this mode is the Modbus ID of the UCM/Modbus. The other Tabs Modbus > Comfort and Alarm> Modbus are not applicable in this mode.
In this mode, third party devices and software are able to control Comfort by sending commands and getting responses. UCM/Modbus is a Slave and the Modbus device is Master. In Comfigurator, the Modbus Master/Slave is set to Server/Slave. The Modbus ID field applies to the UCM/Modbus Modbus ID as a Slave.
The following Modbus functions are supported
Function Code Function Parameters
1 Read Coils Read from starting address, no of addresses
2 Read Discrete Inputs Read from starting address, no of addresses
3 Read Holding Registers Read from starting address, no of addresses
4 Read Input Registers Read from starting address, no of addresses
5 Write Single Coil Write from Address, Value
6 Write Holding Register Write from Address, Value
Write Multiple Coils and Write Multiple Holding Registers are not supported
When Modbus Slave is selected, the screen below should be seen in the Modbus Server Tab
This is a convenient lookup reference table which shows the Modbus Addresses in Decimal and Hexadecimal format of all the Comfort events and registers that are exposed to Modbus.
Each of the items above is a Category that can be expanded by selecting the item
Zones/Inputs
Comfort Zones/Inputs are mapped to Modbus discrete Inputs
Outputs
Comfort Outputs are mapped to Modbus Coils
Flags
Comfort Flags are mapped to Modbus Discrete Inputs
Bypass Inputs
Bypass Inputs are mapped to Modbus Coils.
Counters
Comfort Counters are mapped to Modbus Holding Registers
Sensors
Comfort sensors are mapped to Modbus Holding Regsters
Security/Keypad commands
Key arm security and Autoarm security commands to Comfort are mapped to Holding Registers
Last edited on Thursday Mar 30th, 2017 05:13 pm by slychiu
|
Posted: Thursday Mar 30th, 2017 05:18 pm |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
Notes for Modbus/TCP Slave Mode
For Modbus/TCP, the Modbus Master is also referred to as Client, and the Slave as Server. A Modbus/TCP Slave has an IP address and Port. The Modbus/TCP Master (which is the other device communicating with the UCM/Modbus) should set the Target IP and Port to the UCM/Modbus.
For Modbus/TCP, the Modbus Master is also referred to as Client, and the Slave as Server. A Modbus/TCP Slave has an IP address and Port. The Modbus/TCP Master (which is the other device communicating with the UCM/Modbus) should set the Target IP and Port to the UCM/Modbus.
If Modbus/TCP is used for the Server/Slave, the Properties page shall show a link to Comfort Server Manager
The Comfort Server Manager screenshots below show Modbus Slave (10.0.0.188), along with other ETH03 which may be in the same network (which can be ignored). Note that the Modbus ETH03 should show Universal firmware 1.16
For the UCM/Modbus Slave, select the ETH03 on the left pane. Look at the IP address parameters on the right pane.
DHCP checkbox – This determines if the IP address for UCM/Modbus is to be assigned automatically by the DHCP server.
For Transport Protocol, select “TCPâ€.
For Routing Mode, select “Serverâ€.
In Port 1, select the port number of the UCM/Modbus Server/Slave.
For the other modbus device which acts as the Master (client), enter the IP Address and Port number of the Slave (Server), in this example, 10.0.0.188 Port 1005. This will allow the external Modbus Master to talk to the Modbus Slave via the IP address and Port. Note that the Modbus Master must also comply to the Modbus/TCP standard in order to work with UCM/Modbus as Slave.
Last edited on Monday Dec 11th, 2017 11:21 am by slychiu
|