Comfort  Automation/ Security System Forums Home
Home Search search Menu menu Not logged in - Login | Register

UCM/Modbus as Slave
 Moderated by: slychiu
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Thursday Mar 30th, 2017 05:08 pm
   PM  Quote  Reply 
1st Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

In UCM/Modbus Properties, set Modbus Master/Slave as Slave. Modbus Slave ID in this mode is the Modbus ID of the UCM/Modbus. The other Tabs Modbus > Comfort and Alarm> Modbus are not applicable in this mode.

In this mode, third party devices and software are able to control Comfort by sending commands and getting responses.  UCM/Modbus is a Slave and the Modbus device is Master. In Comfigurator, the Modbus Master/Slave is set to Server/Slave. The Modbus ID field applies to the UCM/Modbus Modbus ID as a Slave.
The following Modbus functions are supported

Function Code  Function                        Parameters
1                       Read Coils                      Read from starting address, no of addresses
2                       Read Discrete Inputs     Read from starting address, no of addresses
3                       Read Holding Registers  Read from starting address, no of addresses
4                       Read Input Registers     Read from starting address, no of addresses
5                       Write Single Coil            Write from Address, Value
6                       Write Holding Register   Write from Address, Value


Write Multiple Coils and Write Multiple Holding Registers are not supported


When Modbus Slave is selected, the screen below should be seen in the Modbus Server Tab
This is a convenient lookup reference table which shows the Modbus Addresses  in Decimal and Hexadecimal format of all the Comfort events and registers that are exposed to Modbus.






Each of the items above is a Category that can be expanded by selecting the item


Zones/Inputs
Comfort Zones/Inputs are mapped to Modbus discrete Inputs





Outputs
Comfort Outputs are mapped to Modbus Coils



Flags
Comfort Flags are mapped to Modbus Discrete Inputs




Bypass Inputs
Bypass Inputs are mapped to Modbus Coils.




Counters
Comfort Counters are mapped to Modbus Holding Registers




Sensors
Comfort sensors are mapped to Modbus Holding Regsters




Security/Keypad commands
Key arm security and Autoarm security commands to Comfort are mapped to Holding Registers




Last edited on Thursday Mar 30th, 2017 05:13 pm by slychiu



 Posted: Thursday Mar 30th, 2017 05:18 pm
   PM  Quote  Reply 
2nd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

Notes for Modbus/TCP Slave Mode

For Modbus/TCP, the Modbus Master is also referred to as Client, and the Slave as  Server.  A Modbus/TCP Slave has an IP address and Port. The Modbus/TCP Master (which is the other device communicating with the UCM/Modbus) should set the Target IP and Port to the UCM/Modbus.

For Modbus/TCP, the Modbus Master is also referred to as Client, and the Slave as Server.  A Modbus/TCP Slave has an IP address and Port. The Modbus/TCP Master (which is the other device communicating with the UCM/Modbus) should set the Target IP and Port to the UCM/Modbus.
If Modbus/TCP is used for the Server/Slave, the Properties page shall show a link to Comfort Server Manager

The Comfort Server Manager screenshots below show Modbus Slave (10.0.0.188), along with other ETH03 which may be in the same network (which can be ignored). Note that the Modbus ETH03 should show Universal firmware 1.16
For the UCM/Modbus Slave, select the ETH03 on the left pane. Look at the IP address parameters on the right pane.




DHCP checkbox – This determines if the IP address for UCM/Modbus is to be assigned automatically by the DHCP server.
For Transport Protocol, select “TCP”.
For Routing Mode, select “Server”.
In Port 1, select the port number of the UCM/Modbus Server/Slave.

For the other modbus device which acts as the Master (client), enter the IP Address and Port number of the Slave (Server), in this example, 10.0.0.188 Port 1005. This will allow the external Modbus Master to talk to the Modbus Slave via the IP address and Port. Note that the Modbus Master must also comply to the Modbus/TCP standard in order to work with UCM/Modbus as Slave.



Last edited on Monday Dec 11th, 2017 11:21 am by slychiu



 Posted: Monday Dec 11th, 2017 12:00 pm
   PM  Quote  Reply 
3rd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top


QModbusMaster is an excellent software tool for testing UCM/Modbus in Slave Mode
Download from https://sourceforge.net/projects/qmodmaster/

This can work in RTU (RS485) and TCP Mode to complement UCM/Modbbus in RS485 and TCP Mode





There is also a related tool for simulating Modbus Slave
https://sourceforge.net/projects/pymodslave/

This can be used for testing UCM/Modbus in Master Mode. It also works in RTU (RS485 ) and TCP mode

Last edited on Monday Dec 11th, 2017 12:03 pm by slychiu