Hi,
Can ISM007 switch boilers, two port valves or pumps on directly?
Do the relay provide enough to switch these on. If not how can these used?
I am not an electrician just need to understand.
|
Posted: Sunday May 13th, 2018 01:54 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5499 |
Status: |
Offline
|
back to top
|
The relays are rated at 6 amps, so please look at the current rating of the valves to see if the ISM can be used to switch them directly. I expect it should be OK but please confirm
|
Posted: Sunday May 13th, 2018 09:05 am |
|
3rd Post |
John W
UCM Pi Users
Joined: | Wednesday Feb 18th, 2009 |
Location: | United Kingdom |
Posts: | 109 |
Status: |
Offline
|
back to top
|
Honeywell and drayton both draw ubder 3 amps to switch, so you should be fine.
If your not an electrician do you know how to wire the valve ?
Blue and brown energise the motor to switch, grey and orange are the normally open contacts. If you arent using the relay to power something else (such as a pump) You could use the contacts connected only to the ism07 input to confirm if the valve is open or closed.
Hope that helps.
|
Posted: Thursday May 17th, 2018 08:57 pm |
|
4th Post |
MDKKEN
Member
Joined: | Monday Aug 17th, 2009 |
Location: | |
Posts: | 38 |
Status: |
Offline
|
back to top
|
Many thanks for your help.
|
|