Comfort Automation/ Security System Forums > Products > UCM > RS232 UCM not communicating after upgrade to 7.XX |
Moderated by: slychiu |
Author | Post | |||||||||
---|---|---|---|---|---|---|---|---|---|---|
Home Comfort Distributors
|
We have an existing installation that we have recently upgraded for the customer. The set up was using a UCM with an RS232 daughter board to connect to a centralite system. After upgrading the UCM to 7.XX there appears to be no communication out of the UCM. When an RS232 communication is sent...- There is a flashing LED on the main board L10 L11 - NO flashing LED on the UCM D9 and D10 Am I correct in saying that the LED's D9 and D10 should flash when an RS232 communication is sent? |
|||||||||
slychiu Administrator
|
D9 and D10 flash when there is communication woth Comfort on the RS485 busIf D9 and D10 are not blinking there is no comms with ComfortD11 and D12 are for communications with Rs232 |
|||||||||
Home Comfort Distributors
|
More to the point it was working BEFORE i upgraded to 7.XX form 5.XXX Are you able to test this with a 7.XXX version? |
|||||||||
slychiu Administrator
|
Can you send the cclx file to edit "support@cytech.biz" Last edited on Tuesday Mar 19th, 2019 04:17 am by slychiu |
|||||||||
slychiu Administrator
|
The cclx file is OK. Upgrading from UCM v5 to v7 should not affect it. The Responses to send mesages to Centralite should work (but whether the commands to centralite work is not known because we do not have any centralite here). You said that D9 and D10 were not blinking, is that the case? if so then the ucm is not being polled, and that does not have anything to do with the firmware or programming. If that is fixed, then when you send a command to Centralite, the D11 (Red) LED (NOT D9) should blink meaning that a message is being sent to the Rs232 interface. Another suggestion not related to this issue. The programming UCM should always be at UCM ID 1 and any other interface UCM should be ID 2 or more. This is because for UCM ID1 can be removed from the network without causing a Communications Failure alarm. UCMs at other IDs when removed will cause Comms failure alarm |
|||||||||
Home Comfort Distributors
|
Centralite Were you aware that they are no longer manufacturing Centralite litejet or the larger version.... think they went into receivership a couple of years ago. We do have software if anyone is in trouble OR can be upgraded without tooo much hassle to KNX. |
|||||||||
slychiu Administrator
|
I think they were announcing new products in dec 2018 si i would be surprised if they went into receivership |
|||||||||
Home Comfort Distributors
|
so i have a test rig set up mimics the file i sent you on UCM1 (the centralite UCM) ( RS232 daughter board in place but NO RS232 'load") D11 D12 DO NOT flash when I send an RS232 command. Howeveron UCM2 (the network UCM) D11 D12 DO flash when I send an RS232 command. Does the RS232 command get sent universally to all boards and only flashes if it sees an RS232 handshake (even though the response is addressed to only a SINGLE UCM !). |
|||||||||
slychiu Administrator
|
The RS232 command gets sent only to the UCM that is addressed. Your results indicate that you have mixed up the addresses of the UCM 1 and 2. I suggest yiou scan for modules, check which is centralite, check the response and write to Comfort That will sort out the problem |
|||||||||
Home Comfort Distributors
|
My results may indicate that BUT I've DOUBLE checked. The leds on the UCM2 flash when i send a Centralite response which is directed to UCM1. I am using the file i sent you. Are you able to replicate the scenario. I still have set up on bench - |
|||||||||
Home Comfort Distributors
|
the only thing i dont have is somethng on the end of the RS232 daughter board BUT surely the LEDs should blink even if there is nothing to deliver to ! |
|||||||||
slychiu Administrator
|
It appears that you are correct. The later UCM firmware does block the send text message if that UCM is not logged in. A new UCM firmware will fix that The UCM Universal is the UCM of choice when communicating with 3rd party systems as it allows different baud rates for communications |
|||||||||
Home Comfort Distributors
|
YES ! YES! YES!I'm finally correct! No great rush but any idea when the update will be available? Thanks |
|||||||||
Home Comfort Distributors
|
Universal - again agreed and again I'm aware of - HOWEVER this is an existing installation and already programmed by original installer. |
|||||||||
slychiu Administrator
|
Testing now, maybe about 2 weeks after all the ISO9001 procedures are fullfilled |
|||||||||
Home Comfort Distributors
|
Any progress on this yet? |
|||||||||
Home Comfort Distributors
|
Any chance of a beta release? |
|||||||||
slychiu Administrator
|
Yes, UCM 7.119 at http://www.cytech.biz/product_details.php?item_id=220 |
|||||||||
Home Comfort Distributors
|
Thank you |
|||||||||
darnold Member
|
I just came across this post. I have a very similar problem in that my UCM/RS232 board connected to my Dynalite Gateway stopped working when sending Comfort -> Dynalite messages but works fine Dynalite -> Comfort. Should I try this beta version? |
|||||||||
slychiu Administrator
|
Yes please upgrade to UCM 7.119 |
|||||||||
darnold Member
|
Thanks! Lights working again. |