Swiss-Toni UCM Pi Users ![]()
|
I know this is a convoluted way of creating an alarm function using a RIO but due to an inability to lay further wiring to an out building, would it be possible to connect an output of a RIO directly to a zone in comfort or would I have to use a relay from the RIO output to create a Zero voltage contact to connect to the Zone: 1) Preferred sequence: Sensor to RIO input. (secondary) RIO output to a Zone 2) Alternative sequence: Sensor to RIO input, (secondary) RIO output to a relay, relay to a Zone This would be done on a Comfort 9000 Last edited on Friday Jul 16th, 2021 01:54 am by |
|||||||||
slychiu Administrator ![]()
|
You would need to use a relay from RIO Output to Comfort input, as RIO output when turned on doez not pull the voltage all the way to 0 |