Hi Mr Chiu,
I have programmed my zones 25 to 30 to bypass zone using SwitchNO response. They have been working fine for the last 2 years or so. However, last 2 or 3 weeks I realized that bypass switches are no longer working. Now, the system announces these zones as "zone Trouble". As a result, I cannot arm the system. Appreciate your support.

Last edited on Monday Oct 21st, 2024 08:17 am by david8811

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

david8811 wrote: Hi Mr Chiu,
I have programmed my zones 25 to 30 to bypass zone using SwitchNO response. There have been working fine for the last 2 years or so. However, last 2 or 3 weeks I realized that bypass switches are no longer working. Now, the system announces these zones as "zone Trouble". As a result, I cannot arm the system. Appreciate your support.


Zone Trouble means there is a problem with the zone wiring. eg brokenm wiring. Are these zone using EOL resistors? What is the EOL shunts position on these zones. If there are wrng eg set to Double EOL position but the EOL resistors are not connected then you will have zone trouble.
if the shunts are set to NO EOL,. then you can test by disconnecting the zone wires from the zones. and connecting a wire to short and Open the zone, Do you get Zone Trouble?

david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 30
Status: 
Offline

  back to top

I used Comfort configurator to setup the response. Does that required physical EOL resistor to be installed?

Last edited on Monday Oct 21st, 2024 08:43 am by david8811

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

Can you send the cclx file to support@cytech.biz after scanning for modules and saving

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

You cannot paste images in the forum. That does not work  in this forum  You have to attach the image. It is be`st to send the cclx file to suppport@cytech.biz

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

your message cannot be read, it results in garbae, I have deleted them to mak the rest of the posts readable

Last edited on Tuesday Oct 22nd, 2024 01:47 am by slychiu

Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 370
Status: 
Offline

  back to top

clean the terminals where the eol pins are on the panel they oxidise and can cause this issue

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

From your email, you have purchased a new SEM01C without zone shunts but you have connected the old LEM03 (which has zone shunts) to this SEM01C. This caused th LEM03 zones to have zone trouble. You ether need to get a new LEM02B or LEM03B without zone shunts so that it can be compatible with the SEM01C, or connect  2 EOL resistors to every zone in the old LEM03 if you want to keep the old LEM03

david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 30
Status: 
Offline

  back to top

Hi Chiu
Thank you for your response. May i know what is the value of the EOL resistor i need to use?

david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 30
Status: 
Offline

  back to top


Hi Chiu

Can I share the 2.2k resistor between Z25 and Z26 as shown in below diagram?

Attachment: Zone Resistor.jpg (Downloaded 11 times)

Last edited on Tuesday Dec 10th, 2024 12:59 am by david8811

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

No, each zone must have its own 2k2 series resistor

david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 30
Status: 
Offline

  back to top

Chiu,
I have installed each zones separately with 2 EOL resistors connected to the old LEM03. Set the shunts to be away from the terminal blocks. Pressed the reset button. But the problem of Zones Trouble is still not resolved. 
Kindly advise what could be the problem?

Last edited on Friday Dec 20th, 2024 10:40 am by david8811

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5837
Status: 
Offline

  back to top

send t the cclx file to support@cytech.biz after scanning for modules and saving the file

david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 30
Status: 
Offline

  back to top

The cclx file has been sent. Appreciate your support