[user=4834]sppooky[/user] wrote:
Quote:TR- negative tamper return
V- negative supply
ST- negative strobe trigger
V+ positive supply
S- negative sounder trigger
TR- negative tamper return - to TAMP
V- negative supply - to COM
ST- negative strobe trigger - to STR-
V+ positive supply - to +12V
S- negative sounder trigger - to SRN-
Hi thanks for the reply. When I opened the bell box the connections are slightly different to what was stated in the instructions. The 5 wired connections are

ST-
R-
SW-
V+
V-

Does R- go into tamp? What about SW-?

Cheers
There must be some documentation to explain these labels otherwise you will have to do it by trial and error for R- and SW- for tamper and siren -ve


i would think

st- strobe trigger

r- tamper return

sw- siren trigger or tamper switch neg

ve+ pos bell hold

ve- neg bell hold off

scan and post the instructions from the sirenor a photo of the connections  and i can decipher them for you
Hi

Same question, different hardware. The aritech as271 has the following connections:
  • Tamper (2 connections)
    12V
    Siren-
    Strobe-

How to connect to comfort?

I did the following, but cannot test yet because my house is not finished :-)
  • Tamper: dedicated alarm input, must program as tamper alarm
    12V: srn+
    Siren-: srn-
    Strobe-: str-

But maybe the siren is a normal speaker and i should use the spk- and 12vf terminals...


Steef
Your connection seem correct
Do not connect to the SPK terminals of Comfort. External bellboxes are not that way
Anyone has experience in connecting an EDS AS240 siren to Cytech?

The only documentation I have is the one in the following URL:

http://www.unitech.com.tr/upload/KLAVUZ/...40_Eng.pdf

Attached is a picture of the only connections I can see in the SIren. My bet is:

PCM SRN+ ---> SIREN \"+\"
PCM SRN- ---> SIREN \"-\"
PCM STR- ---> SIREN \"B\"

Comfigurator settings are at default on the siren related settings.

I don\'t get any sound on Siren. I can\'t even see the status leds in the Siren blinking.

The siren has a battery module that I can be sure if it is only for backup or for normal operations. Is it possible that the bateries are depleted?

Thanks,
Nino
The photo does not match the connections on the manual
Photo has Tamp , + - B
Manual is SAB, +  - S
You should ask them for the correct manual

The + and - should be from Comfort12V and COM, NOT SRN+ and -
Assuming the B terminal  is siren trigger, this should be connected to SRN-