I want to be able to log zone activations, but without changing their zone types. The reason for this is that I have a Neato (Roomba like robot vacuum) that is setting off the alarm when the house is in away mode. I want to be able to let it run through multiple clean cycles, during multiple days and examine which sensors need to be replaced. Is there a way Comfigurator can be left running in the monitor mode without it timing out? Also in the monitor window it would be really useful if it timestamped everything..
Try ComfortClient, it logs all activities to a daily log file. It\'s also comma separated so you can import into Excel and do some neat stuff there.

Ingo
the UCM/USB will not log out by time
UCM/ETH0x will log out after 2 minutes by default but that can be changed in  the DS Manager or Comfort server manager to value of eisded 0 to never log out

You can also use Bus Monitor in Tools which  has a time stamp, but this may end up with a lot of info because that logs all the cmmunications on the bus