Hi,

I have CBus and Comfort units installed

I am able to communicate  Comfort to CBus using UCM to CBus Module (Firmware v. - 7.068) and able to trigger CBus group address using comfort

But What I want is to use CBus group address to trigger comfort IR1Output1 response to switch on my AC

Please describe if it is possible.

Thankyou
In the Cbus to Comfort tab, you can map Cbus Lighting application group addresses to Comfort Counters eg Group address 1 to Counter 10

Group address 1 turned on will set Counter 10 to 255
Group address 1 turned off will set Counter 10 to 00

Each Counter can be asigned to Counter Response
The counter Response can be programed to send Off and On IR signals to the Aircon

This is explained in UCM/Cbus2 Manual which can be downloaded rfrom https://www.cytech.biz/ucmcbus2_manual.html

Do remember to Write To Comfort, AND write to EEPROM in Cbus 2 tab in order for the program to work

You should also use Current sensors to monitor the state of the Aircon fan coil, This gives an On/Off status to the Comfort Input
In The Physical Inputs Tab in Cbus you can map each Comfort Input to a Cbus Lighting group address
Thus when the aircon is turned on, the zone sends its status to the cbus group address so the Cbus switch status follows the actual state of the aircon, even if the aircon is conttrolled by the handheld remote control

Done it successfully

Thanks