When I put O!0401 into the command line I get output 5 ON.or O!0400 - - output 5 OFF 
Using latest comfigurator and latest firmware
O!0001 however does NOT switch ouptut 1 on !


IS THERE A BUG 

I have just tried another set up with C2 7.11 and an older version of Comfigurator and the same occurred.
HOWEVER
I have also tried the latest version of Comfigurator and a C1 and the command works fine. !
The reason I\'m asking is because Ive just set up some virtual inputs that trigger outputs and they are all over the place ! BUT thats for another post !
OK HOW ON EARTH HAS THIS NOT BEEN PICKED UP SOONER !!!
I\'ve done some more investigation as we have a customer waiting for installation...
Comfort 1 is fine .....
Comfort 2      7.XX onwards.......
By putting the following in the command line O!0301 We get a visual display showing output 4 ON
O!0300 we get a visual display showing output 4 off
Physically the output 3 is working ( not output 4).
If you activate the output from the screen then it visually shows the correct output and triggers the correct output. 
There is no bug in addressing of the outputs, otherwise all the lights and appliances that we control in our office on a daily basis would not be working
It seems more like a stuck address line in the Comfort or OP01
You say controlling Output 4 affects output 5 and Output 7 affects output 8Try each output comand and let us know which output is affected
Quote:By putting the following in the command line O!0301 We get a visual display showing output 4 ON O!0300 we get a visual display showing output 4 off Physically the output 3 is working ( not output 4).
   
I am not sure what you mean by the statement above. what is a \"visual display\"? are you saying output causes another visual display? Then can that visual display\" be the problem?

   
Quote:If you activate the output from the screen then it visually shows the correct output and triggers the correct output.
what do you mean \"If you activate the output from the screen then it visually shows the correct output and triggers the correct output\" what \"screen \" and how does that trigger the correct output if the outputs are not triggered correctly
check all the outputs  


eg Output 1 trigger which output



Output 2 trigger which output etc
That will help diagnose the trouble
 Chiu
ive already spent best part of a xay on this THERE IS A PROBLEM
it occurs on ALL output commands in th command line. Ive tried with several C2 and they all do this . ive tried C1 and it does not.
PLEASE TRY THIS OR GET ONE IF YOUR ENGINERRS TO TRY IT.....
-------------------
open a live configurator session . Go to the output screen and make sure the status tab is ticked so the status of the output is visible.in the command line type O!0401 you will see that output 5 goes to on.

We gave already done that many times and have tested again for your benefit, there is no bug on the outputs. The firmware works correctly


> O!0201
< OK
< OP0201
> O!0200
< OK
< OP0200
> O!0301
< OK
< OP0301
> O!0300
< OK
< OP0300
> O!0401
< OK
< OP0401
> O!0400
< OK
< OP0400
> O!0701
< OK
< OP0701
> O!0801
< OK
< OP0801
> O!0700
< OK
< OP0700
> O!0801
< OK
< OP0801
> O!0800
< OK
< OP0800
We have attached a test lamp to each of the outputs and we can verify that when the output says it turns on, it is actuially on and when the outpout says it is off, it is actually off
Have you actually checked to see if the Actual Outputs are acting corredtly?
Would anyone else like to verify by doing the same test?


can you help everyone by answering the questions that I asked?
You say controlling Output 4 affects output 5 and Output 7 affects output 8Try each output comand and let us know which output is affected
Quote:By putting the following in the command line O!0301 We get a visual display showing output 4 ON O!0300 we get a visual display showing output 4 off Physically the output 3 is working ( not output 4).
   
[color=\"#ff0000\"]I am not sure what you mean by the statement above. what is a \"visual display\"? are you saying output causes another visual display? Then can that visual display\" be the problem?
[/color]
   
Quote:If you activate the output from the screen then it visually shows the correct output and triggers the correct output.
[color=\"#ff0000\"]what do you mean \"If you activate the output from the screen then it visually shows the correct output and triggers the correct output\" what \"screen \" and how does that trigger the correct output if the outputs are not triggered correctly
[/color]
If you do not answer our questions we are unable to determine what is wrong
what you are saying is correct BUT now look at the LIVE comfigurator output screen with ststus ticked you will see that although the command line returns the correct reply the screen shows the next output activated and not the one in the command line. 
That is what I was trying to find out when I asked the questions as i could not understand your problem which you described as a firmware bug agffecting Comfort 1 and 2.

[color=\"#ff0000\"]\"I am not sure what you mean by the statement above. what is a \"visual display\"? are you saying output causes another visual display? Then can that visual display\" be the problem?
[/color]

[color=\"#ff0000\"]what do you mean \"If you activate the output from the screen then it visually shows the correct output and triggers the correct output\" what \"screen \" and how does that trigger the correct output if the outputs are not triggered correctly\"
[/color][color=\"#ff0000\"]
[/color]
A correct description would have helped.
From your latest post we can deduce  that the \"Visual display\" you are referring to the Output status display in Comfigurator and not a 3rd party display

The outputs status when \"show status\" is checked does not show the correct output number. It shows the next output eg Output 4 status is shown as output 5

This is a bug in Comfigurator Output status display, it is not a Comfort firmware bug. The Outputs controlled by Comfort is always correct, but the status display in Comfigurator is wrong. This is a relatively new feature in Comfigurator.
As such it does not make any difference if the Comfort is 1 or 2


[color=\"#ff0000\"]
[/color]
OK
I believe that it DOES make a difference and here is WHY
We are using a KNX UCM in the following way:
We are trying to make KNX activate Comfort outputs to control velux windows.
KNX sends a telegram with an altered group address the group address is mapped to a virtual input ( see screen shot attached).
The virtual input is then associated with an on response to trigger the output.
The end result is that the wrong output is triggered.
.cclx file sent by e-mail