Thanks for the Bus Monitor files. These revealed the cause of the problem. Output 4 was set low when Sensor 3 value was received from the TSM temperature sensor.

In Functions > Thermostats, Output 3 was assigned to the thermostat. However there is an undocumentated feature  where the next output is controlled by the thermostat, so that output 4 was affected.
Hence the problem was not due to timers. Timers are working properly.
To work around the problem use another output other than 4 for the light or assign another output for the thermostat in which the next higher output is not used. The next firmware will fix this bug
Thanks for your patience, persistance and help! Smile