10-22-2023, 05:19 AM
Comfigurator 3.14.1 Changes from 3.13.9
Known Bugs
New Features and Improvements
Known Bugs
- Upgrade firmware for Controller shows \"Cannot Obtain Firmware Information\". Workaround - Please download firmware directly from https://www.cytech.biz/firmware.html Or downgrade to 3.13.9 at https://www.cytech.biz/download_files.php?item_id=1301
- Upgrading KP04, KP06, IRIO, MSM, TSM by Coimfigurator will case an error \"Incompatible File System\" to be displayed. Revert to 3.13.9 as workaround
- The number of IRIO Modules are not correctly detected after scan for modules for CM9001-EMS and CM9001-EMS2
- For UCM/KNX and KNX/Logic in KNX Monitor Mode, when logged in by eth03 in CM9001 telegrams do not appear in KNX Monitor or Learn Mode
- For CM9001-EMS, No of slaves was limited to 3, now it can be increased to 5
- For CM9001-EX, No of slaves was limited to 3. Now it can be increased to 5
- The action Set Virtual Input On/Off could not select Virtual Inputs correctly
- When UCM ID1 is not connected, and Comfigurator is connected to UCM > ID2, Scan for Modules may show an extra UCM ID1 with firmware version 255.255
New Features and Improvements
- For the Register Monitor in Comfort Register, the right Pane Set Value box does not show the value of the register, so that if the value is constantly being updated, entering a new value will not be affected by the read values. The centre pane will show the register values that are updated constantly
- Supports Future UCM ARM processor models