Zone Trouble - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +---- Forum: Troubles (https://www.comfortforums.com/forum-77.html) +---- Thread: Zone Trouble (/thread-1584.html) |
- engmoabel - 09-03-2009 hi , I am using comfort II Ultra firmewire 164. I have a problem i dessigned a circuit to make on and off when i connected it to comfort it worked fine but there is aproblem {Zone Trouble} and what ishall do in this problem . i will give you the pic of the circuit?, and if 2 end resistance is nessecary where i should put them? i measured the voltage drop on zone is a 9 Volte on the terminal of the zone? thanks - ident - 09-03-2009 I am not sure I understand your circuit. Is this giving a contact open/close to Comfort with no voltage? If so then set the zone type as Digital Normallly Open or Closed and set Zone Shunts as Double End of Line - BUT do NOT connect any End of line resistors Digital Zone Types will not report any Zone Trouble - engmoabel - 09-03-2009 Thanks it works fine |