Twin Photoelectric Beam Senors - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +---- Forum: Troubles (https://www.comfortforums.com/forum-77.html) +---- Thread: Twin Photoelectric Beam Senors (/thread-1917.html) |
- dcrera - 07-11-2010 Hi I am installing a set of the twin beam sensor. The system reports a zone 15 trouble. I have alligned the sensors as per the manual. Questions : 1. What zone type (number) should I use ? 2. Do I use the NO or NC contact ? Thanks - slychiu - 07-13-2010 The zone type you use depends on the location and purpose of your active beam sensor. You can use
Zone Trouble means that you have set the zone as Double EOL ie shunts inserted away from terminal block but no EOL or wromg EOL resistors connected - dcrera - 07-13-2010 Hi Thanks, problem sorted. Zone 15 had an incorrect shunt. |