siren output - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +---- Forum: Outputs (https://www.comfortforums.com/forum-71.html) +---- Thread: siren output (/thread-1929.html) |
- engmoabel - 07-22-2010 I am using Comfort Ult, Pc900 firmware version 5.183. I am connecting Comfort PCb, KP03, DP03 , pir and UCM05. when i make test on siren i didn\'t work and i measure the volt on the terminal it 3.7 v and when there is no alarm in idle state it measure the same value, i connect a siren 12v as follow + to srn+ and - to srn- . So please advise me with your comment - slychiu - 07-22-2010 Are you measuring the voltage between SRN+ and SRN- ? and not between SRN - to common If the SRN- is shorted to SRN+ it may damage the siren driver Try disconnecting the siren wiring from SRN- and SRN+ for a few minutes and try again If it still does not work send an email to support@cytech.biz - engmoabel - 07-23-2010 i am already measured the vlot between srn+ and srn- not between srn- and com when i disconnected the siren driver it measured the same number 3.7 V note: when i measured the volt after i reset the system the volt value go up and down between 0 and 12v and after short time it gives the same value 3.7V - slychiu - 07-23-2010 This should be a programming problem. Each Alarmn Type as a setting for Siren Type, and each Siren Type has a setting for whether the Bell output is activated or not Send the cclx file to support@cytech.biz so we can check your program |