Engineer menu - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +---- Forum: Troubles (https://www.comfortforums.com/forum-77.html) +---- Thread: Engineer menu (/thread-3744.html) |
- Home - 03-26-2014 On site yesterday an put a system into engineer test menu 8,6,4 During the course of testing Comfort made several dial outs (which it is supposed to do!). However if it is in test mode surely it should NOT dial out? This leads me onto what is disabled and what is NOT in engineer test mode? For example remote access for UCM\'s, relay out puts to openers etc etc. I\'m never really quite sure = Do you happen to have a list of what is disables (or not) in engineer test mode - thanks - ident - 03-26-2014 Engineer test mode prevents any zone from activating, hence it prevents zone alarms If alarms are not activated then there is no dial out What dial out was activated? It is possible that non detector alarms could cause dial out eg comms failure This feature was implemented very long ago so perhaps the way it works need to be changed Normally we use Security Check F32 which prevents any alarm but announces any zone activated while engineer test mode is silent |