- Vietbao - 10-24-2014

Hi all,I\'m a newcomer and i\'m finding out UCM/KNX, can you give me a program complete for UCM/KNX?Thanks!


- tech07 - 10-25-2014

A simple example of a cclx file with KNX is attached

Go to Modules Tab and select UCM02 (which is normally the KMX UCM id)


The KNX to Comfort screen is shown
Lighting Group addresses 1/1/1 to 1/1/3 are mapped to Counters 1 to 3 in Comfort. This means that the Lighting group states will be kept in the counter when there is any change. eg 0 for off and 255 for on and 1 to 254 for dim levels. The Comfort Control menu can control the KNX  lights



Keypad Key is mapped to 5/1/0 (1 byte object). This allows a KNX touchscreen to have keypad buttons 0 to 9, Enter to simulate the comfort keypad to disarm the security system using the user actual code.
for example



Panic Button is mapped to 5/1/13 (1 bit). This allows a KNX button to trigger a panic alarm.
Arm to Away, Arm to Night, Arm to Day modes are mapped to 1 bit objects

Time and Date are mapped to KNX Date and Time objects so Comfort time (which can be synchronised to Internet Time server via UCM/ETH03) can send its date and time to KNX.

The Comfort to KNX screen is shown below. This is for Comfort alarm conditions sending to KNX.




Zone Status is mapped to 5/1/1. This maps a range of 1 bit group addresses from 5/1/1 to 5/1/96 corresponding to max 96 zones. if Zone 1 opens, the KNX group 5/1/1 will turn on and vice versa. Allow for as many group addresses as there are zones in the system

Zone Not Ready is a 1 bit group address which turns on when the system is being armed but a zone is open

Armed State is 1 bit meaning that the security system is armed, and is off if not armed

Alarm state is 1 bit which is on if th system is in alarm state

Panic state, Tamper state, Line cut, zone trouble, Low Battery, AC Failure are mapped to 1 bit group addresses which signal the condtion in the system




- tech07 - 10-25-2014

The Control Menu is shown




This allows Comfort to control the KNX Lights by setting the mapped counters to 0 for off and 255 for on

The Counter status gives the feedback status for the mapped group address

This control can be done via the Comfort iOS and Andrroid app



- Vietbao - 10-25-2014

Thanks for your help!