ISM07 relay. - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Products (https://www.comfortforums.com/forum-3.html) +--- Forum: IRIO (https://www.comfortforums.com/forum-129.html) +--- Thread: ISM07 relay. (/thread-4887.html) |
- MDKKEN - 05-12-2018 Hi, Can ISM007 switch boilers, two port valves or pumps on directly? Do the relay provide enough to switch these on. If not how can these used? I am not an electrician just need to understand. - slychiu - 05-13-2018 The relays are rated at 6 amps, so please look at the current rating of the valves to see if the ISM can be used to switch them directly. I expect it should be OK but please confirm - John W - 05-13-2018 Honeywell and drayton both draw ubder 3 amps to switch, so you should be fine. If your not an electrician do you know how to wire the valve ? Blue and brown energise the motor to switch, grey and orange are the normally open contacts. If you arent using the relay to power something else (such as a pump) You could use the contacts connected only to the ism07 input to confirm if the valve is open or closed. Hope that helps. - MDKKEN - 05-17-2018 Many thanks for your help.
|