Slave communication failure - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Support (https://www.comfortforums.com/forum-2.html) +--- Forum: Problems & Troubleshooting (https://www.comfortforums.com/forum-36.html) +---- Forum: Troubles (https://www.comfortforums.com/forum-77.html) +---- Thread: Slave communication failure (/thread-928.html) |
- Choppa - 01-19-2008 Hi,I have just installed a minderpro (comfort) system,and I am having problems with the main panel talking with the two slave units I have installed. All it tells me on the keypad that there is a communication failure slave 1 and 2. Can any one help? Thank you. - admin - 01-19-2008 Check the each Slave is set to a different ID. If you have two slaves, the ID should be 1 (A, B, C shorted) and 2 (A open, B,C shorted) - Choppa - 01-28-2008 Thank you so much, worked frist time. |