The wiring diagram shows how to connect most Siren/Bellboxes to Comfort
The diagram is from the Comfort Installation Manual

SRN+ Siren (+) output has  constant 12 volts to be connected to the Siren box.
SRN- Siren (-) output is normally floating, but pulled to ground to activate siren.
The Tamper terminals of the Siren/Bellbox can be connected in series with the Case tamper switches. Alternately the Siren/Bellbox tamper terminals can be connected to a spare zone input on Comfort which is programmed as a Tamper Zone Type.



If the siren/bellbox  sounds softly as soon as  it is connected connect a   pull-up resistor (1K-ohm) placing between the SRN+ and the SRN- 'terminal. If you wish to  work on the siren/bellbox connections or open the control panel, you can  prevent the system from causing a tamper alarm by entering Engineer Test Mode via Eng. Menu 8,6, 1 for on. Upon deselecting this option 8,6 ,0 for Off, the system will enter Security Check Mode and will report any faults through the keypad. Tamper Alarm means the Panel Tamper or Bellbox Tamper switch or Connections are open or incorrect.

Last edited on Saturday Dec 6th, 2014 05:53 am by slychiu



 Posted: Tuesday Jun 26th, 2012 04:23 pm
   
2nd Post
wexfordman
UCM Pi Users
 

Joined: Monday Jan 1st, 2007
Location: Cork, Ireland
Posts: 546
Status: 
Offline

  back to top

Hi,

Any suggestions on why my external bell box strobe is working but no bell?

Regards
Eamon



 Posted: Wednesday Jun 27th, 2012 03:03 am
   
3rd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The of the below possibilities
  1. The bellbox is not working
  2. the siren output is not working
  3. The connections are wrong for the bellbox you used
To check (2) get the alarm to activate and measure the voltage between SRN- and SRN+ using a multimeter. It should be 12V That means voltage is applied to the bell and one of the other 2 possibilties is true



 Posted: Tuesday Aug 28th, 2012 03:43 pm
   
4th Post
auredor
Member
 

Joined: Sunday Feb 19th, 2012
Location:  
Posts: 20
Status: 
Offline

  back to top

Hello,

I've a similar issue.

I've got a siren box that only need to be triggered to be enabled. The siren manages its own melody and includes a battery.

This siren is supply by a power of 14VDC. The trigger should be at 14VDC to keep the siren quiet and goes to 0VDC to enable the siren.

Unfortunately, using SRN+, SRN- and STR- doesn't provide enough voltage (12VDC max) to keep the siren disable. So today, I've to use a standard output of the Comfort in ON state with one wire not on the common and the second wire on the supply from the comfort to get 13VDC what is enough to keep it quiet. However I'had to manage this output "manually" and reprogram (enabling, disabling, siren duration...) the Comfort to get a similar behaviour than using directly the dedicated output. This is not perfect but it works. Obviousl I would prefer to do in a cleaner way because there is still some featues that I don't have resimulated. Any idea?

I though to use a relay with the 14VDC power supply transformer. But if the general power supply faild, it means that the siren will be enabled although there is no intrusion.  



 Posted: Wednesday Aug 29th, 2012 02:12 am
   
5th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

It is not that the SRN does not supply enough 12V.
The SRN +/SRN- outputs will turn on 12V when the alarm triggers so it is the opposite of what you are trying  to get.

If you want the reverse, ie the siren voltage to turn on when there is NO alarm, and voltage off when there is alarm, then go to Configuration > Modules a& Settings>  and enable  Siren Reverse then write to Comfort




 Posted: Wednesday Aug 29th, 2012 07:44 am
   
6th Post
auredor
Member
 

Joined: Sunday Feb 19th, 2012
Location:  
Posts: 20
Status: 
Offline

  back to top

I've changed this configuration but the voltage is not high enough (checked 12VDC with voltmeter) and the siren doesn't remain disable.



 Posted: Wednesday Aug 29th, 2012 12:42 pm
   
7th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

What exactly is the voltage when there is no alarm?
what is the voltage when there is an alarm?




 Posted: Wednesday Aug 29th, 2012 02:15 pm
   
8th Post
auredor
Member
 

Joined: Sunday Feb 19th, 2012
Location:  
Posts: 20
Status: 
Offline

  back to top

At 12VDC the siren is switched on

Above 13VDC the siren switches off.



 Posted: Thursday Aug 30th, 2012 01:48 am
   
9th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

If the siren switches off only above 13V that shows that there is something wrong with the siren, or it is not suitable for alarm systems which supply 12V

With the AC off, the alarm is powered by the battery until 11V

Last edited on Thursday Aug 30th, 2012 02:10 am by ident



 Posted: Friday Nov 30th, 2012 08:55 pm
   
10th Post
gimi
Member
 

Joined: Saturday Jun 2nd, 2012
Location:  
Posts: 15
Status: 
Offline

  back to top

Hello,

I purchased the GE AS6430 siren system which I want to connect to Confort but following the attached diagram, I am not sure the below connection are right:
Confort - AS630
SRN+ - 3
SRN- - 2
STR- - 1
12VF - ???

Thank you in advance for your support.

Mihai.

Attachment: GE AS630 connection diagram.jpg (Downloaded 219 times)



 Posted: Saturday Dec 1st, 2012 12:25 am
   
11th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

what a complicated diagram
I would guess
SRN+ Open (it is also 12V supply)
SRN- - 2
STR- - 1
12VF - 3
COM - 4






 Posted: Saturday Dec 1st, 2012 03:35 pm
   
12th Post
gimi
Member
 

Joined: Saturday Jun 2nd, 2012
Location:  
Posts: 15
Status: 
Offline

  back to top

Thanks Ident,

Close guess but unfortunately as soon as I power on the alarm the siren starts buzzing! Just FYI, I do not use the Comfort tamper.

Mihai.



 Posted: Saturday Dec 1st, 2012 10:10 pm
   
13th Post
wiredhome
Comfort Distributors


Joined: Thursday Apr 12th, 2007
Location: Dublin, Ireland
Posts: 81
Status: 
Offline

  back to top

I think you need to cut J4 & J6



 Posted: Monday Dec 3rd, 2012 09:16 pm
   
14th Post
gimi
Member
 

Joined: Saturday Jun 2nd, 2012
Location:  
Posts: 15
Status: 
Offline

  back to top

Hi there,

Thanks for your involvement. Cutting the jumpers is not the same as connecting the cable to different outputs therefore I would like to ensure I cut the rights ones.

Just to check if I well understood the diagram. By cutting the J4 and J6 it means the siren will switch on when the input signal will switch from 12VDC to 0VDC, right? Just FYI, I do not use the siren internal battery thus the J3 is cut. Having the J3 already off it is not the J5 and J7 I have to cut? I expect GE to care of energy consumption and not keeping continuous 12VDC on the siren.

Cheers,
Mihai.



 Posted: Tuesday Dec 4th, 2012 11:38 am
   
15th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

Comfort wil pull down the Siren and Strobe Outputs  to turn the respective device on, so wiredhome should be correct to say J4 and J6 should be cut

This should be regardless of whether you use the internal battery or not
If the internal battery is used, the siren will sound when the 12V voltage from Comfort is disconected. At least that is how I understand it



 Posted: Saturday Dec 8th, 2012 06:24 pm
   
16th Post
gimi
Member
 

Joined: Saturday Jun 2nd, 2012
Location:  
Posts: 15
Status: 
Offline

  back to top

Dear ident and wiredhome,

Thank you very much for your support. Unfortunately by cutting J4 and J6 I got the same behavior as before, as soon the power of the Comfort is on the siren and strobe are on and remains like this even after the security off message (thus Comfort doesn't send any alarm messages). FYI,the Comfort tamper is in loop as I do not use it. The GE siren 5 and 6 connectors are not connected. Should I try the J5 and J7 as I do not see other combination as long as the connections with the Comfort are OK?

Cheers,
Mihai.



 Posted: Sunday Dec 9th, 2012 02:29 am
   
17th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

No, I dont think J5 and J7 should be cut
Try Connecting a 1K resistor between the 12V and Siren and between 12V and Strobe terminals as shown in their diagram



 Posted: Tuesday Dec 18th, 2012 04:32 pm
   
18th Post
gimi
Member
 

Joined: Saturday Jun 2nd, 2012
Location:  
Posts: 15
Status: 
Offline

  back to top

Thanks! Adding the resistor solved my issue!

Strange enough for GE not to provide a resistor taking in consideration it is required.

Cheers,
Mihai.



 Posted: Wednesday Dec 19th, 2012 09:38 am
   
19th Post
wiredhome
Comfort Distributors


Joined: Thursday Apr 12th, 2007
Location: Dublin, Ireland
Posts: 81
Status: 
Offline

  back to top

The resistors are provided with the GE Panels



 Posted: Sunday Mar 17th, 2013 08:04 pm
   
20th Post
sppooky
Member
 

Joined: Friday Dec 21st, 2012
Location:  
Posts: 11
Status: 
Offline

  back to top

Hi I wonder if anyone can help me. I'm just completing final installation of comfort alarm system and just got bellbox to connect. It's a Honeywell AG6 external sounder and strobe. Can anyone tell me where, on the comfort panel, I need to connect the following connections:-

TR- negative tamper return
V- negative supply
ST- negative strobe trigger
V+ positive supply
S- negative sounder trigger

Thanks
Rikki