Combi Boiler switching
#1
Hoi may be a stupid question, I am going to be having a comfort system installed soon, I would like to have my central heating also within my home automation, I currently have a C-Bus system in  place and know that my boiler needs a volt free thermostat.

I have looked at the c-bus option and a thermostat is £100 aprox which i fine but the volt free relay is almost £400.

My question is can the same job be done with the C-bus thermostat & the RLY01 from Comfort? as this would make italot more affordable.Or can anyone suggest a more affordable option.

Thanks
Reply

#2
What is the specifications of the volt - free relay that is needed, ie coil voltage andn contact rating?

How does the Cbus thermostat connect to the volt free relay?
Reply

#3
hi all the boiler manual says is to use a volt free thermostat, it is a two wire type, the c-bus and comfort would be connected using ucm cbus
Reply

#4
You can probably use the RLY01, if the Cbus Thermostat can drive the RLY01. The RLY01 requires a 12V output to turn on the relay, so if the Cbus thermostat is able to supply that then it should work
Reply

#5
I use this, but CBUS takes care of the voltage free switching. Comfort controls the logic.

I also installed a 2 way switch, so I can manually switch between CBUS control and the old central heating timer (for testing).

Fairly simple - as my old central heating timer had all the info I needed.
Reply