10-17-2006, 03:45 PM
Help!!!
System config:
Comfort I Ultra
Action 4.227
Three SEM01\'s (2 with firmware 4.177 & one 4.178)
Four LEM01s
Four UCM\'s (IR 5.63, ETH 5.79, GSM 5.68, CWM 5.70)
Comfigurator 2.1.0
Battery Warning 35 is reported on sign-in and after system reset (Event log shows Low Battery #Slave 3).
CPU and each SEM has its own power supply/battery. Have replaced slave 3\'s battery, swopped it with slave 2\'s battery, checked the battery voltage - according to my meter it drops from approx 13.84 to 13.78V in about 3 minutes with the AC power disconnected.
Slave addresses are correct. Comfigurator is set for 3 slaves.
Have also tried to set Battery Test Interval and Battery Test Duration to 0.
KA/KB is wired from CPU to slave 1 (approx 15 metres), from CPU to slave 2 (approx 20 metres), and from slave 1 to slave 3 (approx 30 metres). COM is commoned between the CPU and the 3 slaves. All cabling is STP.
Have been running slaves 1 & 2 for some time and have recently added slave 3.
Interestingly, and I don\'t know if this has anything to do with the problem - when slave 3 is added, the \"Security off\" announcement after system reset gets shortened to \"curity off\". Remove slave 3 and we have \"Security off\" again!
Slave #3 has formware 4.178 and the others have 4.177.
Access to the slaves is a little difficult, so, before I swap around two slaves to see where the problem goes, does anyone have some advice on what else to try?
Thanks,
Leon
--
Leon Schutte (leons@opentech.co.za), Cell +27 82 780-8872
OpenTech, Tel +27 31 467-2983, Fax +27 31 467-1116
System config:
Comfort I Ultra
Action 4.227
Three SEM01\'s (2 with firmware 4.177 & one 4.178)
Four LEM01s
Four UCM\'s (IR 5.63, ETH 5.79, GSM 5.68, CWM 5.70)
Comfigurator 2.1.0
Battery Warning 35 is reported on sign-in and after system reset (Event log shows Low Battery #Slave 3).
CPU and each SEM has its own power supply/battery. Have replaced slave 3\'s battery, swopped it with slave 2\'s battery, checked the battery voltage - according to my meter it drops from approx 13.84 to 13.78V in about 3 minutes with the AC power disconnected.
Slave addresses are correct. Comfigurator is set for 3 slaves.
Have also tried to set Battery Test Interval and Battery Test Duration to 0.
KA/KB is wired from CPU to slave 1 (approx 15 metres), from CPU to slave 2 (approx 20 metres), and from slave 1 to slave 3 (approx 30 metres). COM is commoned between the CPU and the 3 slaves. All cabling is STP.
Have been running slaves 1 & 2 for some time and have recently added slave 3.
Interestingly, and I don\'t know if this has anything to do with the problem - when slave 3 is added, the \"Security off\" announcement after system reset gets shortened to \"curity off\". Remove slave 3 and we have \"Security off\" again!
Slave #3 has formware 4.178 and the others have 4.177.
Access to the slaves is a little difficult, so, before I swap around two slaves to see where the problem goes, does anyone have some advice on what else to try?
Thanks,
Leon
--