The \"phantom Keypad\" is produced by the following conditions

  1. The cclx file had a keypad eg KP04 in the modules tab say at ID 1
  2. Scanning of modules detects that there is a different keypad at the same ID say KT03
  3. The KP04 that was not found is not deleted from the configuration. Instead it is moved to the last (unused) ID and marked in Red as \"Not found\". you can now delete it manually. The reason for this is that some modules have programmed  data like KT03, UCM/KNX etc with data. If the module was temporarily removed for testing, we do not want to delete the programed data, so the module is not deleted automatically.
For Firmware upgrade, right click on the module should show the firmware upgrade options



Transfer > Firmware Upgrades is for firmware upgrade by programmng cable for firmware < version 6


Reply

#12
Update

Right clicking on keypads will not show the options to upgrade firmware if the module after scanning is \"not found\" ie in red
That means the scan was unable to detect the keypad, hence it would not be possible to upgrade its firmware. The KT03 was not found perhaps because its ID was set to FF ie unassigned. Older KT03 firmware may have a problem of having the ID reset to FF
Upgrading to KT03 7.032 will probably fix this issue