Help needed with bypass action
#1
Trying to do a response where a PIR in zone A under specific conditions triggers bypass of zone B and then a PIR in zone B triggers bypass of zone C. But the bypass appears to do exactly that - bypass completely so the PIR in zone B doesn\'t report to Comfort and so the bypass of zone C never happens.

I suppose this is sort of logical, but was just wondering if this is the correct behaviour or whether I\'ve got something wrong in my code.

I could probably do this using a timer or simply bypass zones B and C from the zone A trigger, but would like other automation functions to continue to operate - for example, lights off and unbypass in zone C after a specified period of inactivity. Is this possible? I suppose I could also put in additional \"non-alarm\" PIRs, but this seems to be a waste of inputs!

Reply

#2
Bypass means the zone is ignored completely
You may be able to accomplish what you want by setting a Flag for the zone which is checked in the zone response and Skips the alarm
The zone response based on Time can also set Flags in other zones etc

Reply

#3
Thanks for your reply Chiu.

Hadn\'t used Skip Alarm before but had been considering trying this and your reply gave me the necessary kickstart. Have set the zone-on response to check a flag before doing what needs to be done and set & unset the flag in other responses as needed. Also had to use Skip Announcement and now this appears to do exactly what I wanted. Once again thanks for your ever present assistance.

Regards,